    york experts! ...desperate!



    I have a double twin compressor set up giving me trouble...this set up does not have a low ambient kit on it. The part that will make you chukkle is that this set up is in mn.

    Well if you want to help me with low discharge superheats and an or an economically feasable alternative to screws let me know.

    This chiller set up is for a plating. Process. It spends 90 percent of time u.der 30% maintaining 19 deg on 134. There is only a 900 gallon glycol tank.

    I feel system should be at least 10,000 gallon silo for this set up as when they start plating on syzstem it instantly throws 1850 watts at system and can not ramp up fast enough to handle the shock. I feel we need a large buffer vessel...our engineer disagrees.

    HATE INTRODUCING MYSELF THIS WAY...BUT HELLO FROM MINNESOTA EVERYONE WITH MEASURED AMBIENT OF 24 DEGREES

    BRAD



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: york experts! ...desperate!

    Hi Brad,

    I don't work on chillers so won't be much help, hopefully some more knowledgeable members will be along shortly.

    Does sound like the buffer vessel is too small if the temperature rises too much before the chiller can respond.
    What is your engineers solution to the problem seeing as they disagree?

    Jon
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: york experts! ...desperate!

    Brad,
    If you have t/stat in return line before buffer tank it can respond much earlier to maintain temps.
    It will sense temp much sooner & ramp up.

    What controls are you currently using & how is it set up.

  4. #4
    Join Date
    Mar 2013
    Location
    Malaysia
    Posts
    2
    Rep Power
    0

    Re: york experts! ...desperate!

    Hi Hello there,
    Does anyone knows where to find the complete troubleshooting guidelines for YORK.

    TQ

  5. #5
    Join Date
    Dec 2012
    Location
    Kuwait
    Age
    59
    Posts
    30
    Rep Power
    0

    Re: york experts! ...desperate!

    Quote Originally Posted by aharaz View Post
    Hi Hello there,
    Does anyone knows where to find the complete troubleshooting guidelines for YORK.

    TQ
    Hi,
    I can send you the manual for air cooled chiller unit where you can go thro the trouble shooting chart. if required pl mail me.
    tvrao161@hotmail.com

    regards
    tvrao

  6. #6
    Join Date
    Mar 2013
    Location
    Malaysia
    Posts
    2
    Rep Power
    0

    Re: york experts! ...desperate!

    Quote Originally Posted by tvrao View Post
    Hi,
    I can send you the manual for air cooled chiller unit where you can go thro the trouble shooting chart. if required pl mail me.
    tvrao161@hotmail.com

    regards
    tvrao

    Hi Mr Tvrao,

    Pl check yr mail.

    Thanks

    Regards
    aharaz

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: york experts! ...desperate!

    Gruntzilla

    Is it an air cooled screw package, ycas or yaes?

    Sounds like you're right with buffer tank, these are hvac chillers and may be too slow to react when sudden load is thrown at them.

    alec
    Mostly found in the southern part of this green and pleasant land.

  8. #8
    Join Date
    Jan 2010
    Location
    india
    Posts
    35
    Rep Power
    0

    Re: york experts! ...desperate!

    Dear Brad,

    What type of evaporator is there( Dx, pump feed , gravity feed)
    You can adjust your chiller compressor loading time.