    Low pressure receiver in DX system



    Dear All,

    Please have a look at the attached drawing.

    Any body used or seen this system?

    The low pressure receiver acts as a flash gas removal tool (it seems).

    Any practical problems using this system ?

    Appreciate any input.

    Cheers,
    LANA
    Attached Files Attached Files


    Even Einstein Asked Questions

  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Low pressure receiver in DX system

    the receiver will freezt frost and how are controlling the liquid into the evap

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Low pressure receiver in DX system

    Thanks for the reply.

    That's why I raised the question.

    I have seen this on a mini water chiller catalouge (not seen it on action).

    Any more inputs will be great.
    Cheers
    LANA
    Even Einstein Asked Questions

  4. #4
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: Low pressure receiver in DX system

    I have seen this type of low pressure receiver use at new York screw chillers (MODEL YCIV) mention flash tank by controlling with two electronic expansion valve. So the main purpose of this to remove the flash gas, same like economizer using for centrifugal chillers. As per your catalogue, there is not low side expansion device and why use for this mini chiller.

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Low pressure receiver in DX system

    This is not complete drawing. Suction from LPR should be connected to the compressor. LPR should be insulated. Liquid pump should supply liquid to the evaporator.

  6. #6
    Join Date
    Jan 2013
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Re: Low pressure receiver in DX system

    Would that be a DX system with no expansion device between the receiver and the evaporator ?

    Wouldn't it be more like a flooded evaporator system ?

  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Low pressure receiver in DX system

    Thanks guys for the inputs.

    The drawing I saw is like the drawing I sent. All the replies seem correct that's why I am confused. We have this in liquid circulation system with liquid pump BUT on a DX??? Something is wrong I think!!!

    Thanks again
    Even Einstein Asked Questions

  8. #8
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Low pressure receiver in DX system

    It is not problem to use liquid pump for DX coil. However, when you throttle refrigerant to LPR flash gas will be created If you don't have suction line, how this gas can be removed.