    Unhappy Toshiba vrf !!!! Help



    Hi fellas , I'm a big stuffed as I have a call out tomorrow to a toshiba vrf 410 system , now all I'm told is that some rooms are showing an L20 fault ?
    I'm used to working with daikin and don't have a clue what an. L20 is or how to possible rectify it... And tosh tech won't be open on Saturdays !!!
    So I'm relying on you lot to help me out here .. Please !!!



  2. #2
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Toshiba vrf !!!! Help

    By the way the model for outdoor is mmy-map080ft8-e if that helps

  3. #3
    Join Date
    Jan 2009
    Location
    england
    Posts
    17
    Rep Power
    0

    Re: Toshiba vrf !!!! Help

    L20 is a duplicated centralized control address. email me dangcornish@hotmail.com if you want the service manual

  4. #4
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Toshiba vrf !!!! Help

    I know that this site does not have a centralised controller , all seperate bedroom controls , no bms also

  5. #5
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Toshiba vrf !!!! Help

    Any help in solving the problem would help and why this may of happened ??

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba vrf !!!! Help


  7. #7
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Toshiba vrf !!!! Help

    L20 – – 98
    AI-NET
    Indoor
    unit
    Duplicated
    central control
    address
    All stop There is duplication in central
    control address setting.
    • Check central control
    addresses.
    • Check network adaptor
    P.C. board (applicable to
    AI-NET).

    1 . You are precisely sure, what there is no central panel? And schedulings...
    2 . As far as the quantity of indexes of internal blocks differs from a possible maximum of 130%
    3 . You tried to make automatic readdressing?

  8. #8
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Toshiba vrf !!!! Help

    Yeah iv had a look at service manual , but dunno what the addresses would be , I know this site has no paperwork commissioning sheets

  9. #9
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Toshiba vrf !!!! Help

    There is no central control !! I know that as I done the maintenance thee at Xmas , all workin fine then , how could a duplicate happen ??? Automatic re addressing ? What is that and how ? And number 2 on your quote rusbuka what's that mean , pardon me if I sound s little thick but don't have much experience with tosh

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba vrf !!!! Help

    if theres no commissioning info on site- start mapping out addresses on units- sometimes ur lucky and the install monkey has scribbled the addresses on the indoors- shouldn't take u too long to find out which address is duplicated- hopefully theres a local remote with a flashy light on it- hopefully there aint 64 indoors where a muppet has been tinkering!!! -good luck

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Toshiba vrf !!!! Help

    If capasity of indoor units more outdoor 130%, on site was problems.
    Dip sometimes dont help. Simply try to dump everything, and to make automatic addressing on the new.