    Mar 2012
    philippines
    2
    frost on compressor
    HI,
    I have a carrier primeline 69NT40-561 scroll compressor
    compressor was covered with frost and pulled down temp at -15C only
    supply temp and return temp sometimes equalizes
    2 alarms flashes on the screen
    alarm 67 and 66
    anyone willing to share idea on this problem
    thanks
    Feb 2007
    2,477
    Re: frost on compressor
    If the compressor itself is "covered with frost" then you haven't got enough superheat, check super heat and adjust/replace TEV/EEV/metering device as neccessary.
    70
    10,650
    52
    I see that your areas humidity is between 45% to 80%, with a -15C suction temperature you would expect some frosting on the cold surfaces.
    May 2011
    India
    32
    93
    8
    Even -15 degree C suction temperature indicates that there is a chance of liquid refrfigerent being sucked in... Better check the load and refrigerent superheat, else you will end up killing the compressor.
    44
    3,803
    Air flow across evaporator? No load on a system will result in low superheat and possible frosting on compressor body.
    Jan 2008
    north west
    36
    234
    13
    Frosting on the compressor can also be caused by over charged with refrigerant.