    Re: twin wire with shielded cable

    Hi guys
    First up this topic should be in the controls section.
    Frikkie You are right, we can and do on some systems send data over power. In NZ some domestic hot water systems switch off and on from signals an the power line, called the ripple system. Not sure why we don't use it more in controls. I am working on a new system using the Arduino controller and will try to incorporate this function to save wiring - the idea is to use smart sensors and all I/O so as to communicate to blocks and sub blocks with LAN (not sending out 0 - 10v) but communicating to an address and sub address with data. Have become very busy at work though
    Hi Al with most newer units of the same brand will either have a lon (echlon) chip on the controls board or lan for such a purpose to communicate off/on and a limited amount of other points. Here you can daisy chain a bunch of units on site and connect them up to a HLI like tridium, opc which can then relay this data to a BMS. I only know of one person who has done it.

  2. #2
    Join Date
    Jun 2010
    Location
    geraldton western australia
    Age
    39
    Posts
    57
    Rep Power
    14

    Re: twin wire with shielded cable

    Quote Originally Posted by Tesla View Post
    Hi guys
    Frikkie You are right, we can and do on some systems send data over power.
    hitachi 2.5 and 3.5kW wall splits only use a 2 wire 35VDC interconnecting for power and comms between indoor and outdoor unit.