FYI , Biflow driers and Reversing valves.
I had an issue with a package A/C unit this week. In cooling pressures were normal , switch to heating and with in 10 seconds unit running in to vac . My thought was the expansion valve faulty but these were accurators and all moving and seals all ok. Next on the list was RV , what a mission to change (1 3/8 tubing)! the boss said i ll order one and you change it. I thought about it and asked about the bi flow filter could be blocked in one direction , No said boss.
So thought , ill just change filter first so i cut out the bi flow first and replacing and vac down the system , charge it up and run it , sure enough it was the filter check valve faulty , i could blow through one end but not the other.
Just something else to check out when diagnosing i quess.
Cheers Andy
-
06-03-2013, 08:16 PM #2
Re: FYI , Biflow driers and Reversing valves.
Very interesting! What make and model were the driers and what where they fitted too? Just had same problem...
http://www.youtube.com/watch?v=6pUZBi38rCM
Cheers JonMostly found in Oxfordshire, UK :)
-
07-03-2013, 03:12 AM #3
Re: FYI , Biflow driers and Reversing valves.
Hey Monkey, they were an emerson filter drier , not sure of exact details, 5/8 solder . The unit was a Temperzone package, New Zealand made.
-
07-03-2013, 03:31 AM #4
Re: FYI , Biflow driers and Reversing valves.
Just seen your video and the drier i replaced it with was a Sporlan ! dooh
-
07-03-2013, 08:11 AM #5
Re: FYI , Biflow driers and Reversing valves.
Last edited by mikeref; 07-03-2013 at 08:13 AM. Reason: Unable to give you points..... or cheese. Sorry.
To the optimist, the glass is half full. To the pessimist, the glass is half empty.
-