    Compressor Short Cycling



    Hello fellow engineers,
    I've recently come across a problem with my two door Skope freezer which has a specially designed unit with a Danfoss compressor on it. I've noticed the compressor was short cycling after bringing the cabinet temperature down as far as negative 3 degrees celcius and would'nt go any futher after which i thoroughly cleaned the condensor and hence this gives the compressor ample time to cool down after being switched off. I initially suspected the start capacitor but then i have my doubts due to it working fine in the first place. What else could the cause of this be?



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    504
    Rep Power
    21

    Re: Compressor Short Cycling

    is the system short of refrigerant

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Compressor Short Cycling

    Need to know why compressor is stopping. Does it still have power when it stops? Which would point to compressor or refrigerant problems. Or does the power cut off which would point to control issues.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Jan 2007
    Location
    New Zealand
    Age
    42
    Posts
    50
    Rep Power
    18

    Re: Compressor Short Cycling

    Being a Scope, It will have a Carel controller, you'll have to make sure the controller is actually asking for the compressor to run, test the compressor output from the controller too prove its not faulty, or has the incorrect setpoint.
    Then move onto the compressor (relay, start cap etc)

  5. #5
    Join Date
    Mar 2013
    Location
    Fiji
    Age
    42
    Posts
    2
    Rep Power
    0

    Re: Compressor Short Cycling

    Thanks friends, unit was a little over charged so i recovered the refrigerant, changed the drier, removed the old oil and fill new oil, flushed the line, vaccumed the unit and re-charged the system. It's working fine so far and cuts off at -18 degrees. Charged mostly liquid R404. controller seems to be programmed ok according to Specs.

    Thanks guys!

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor Short Cycling

    Thank you so much for the status update, glad to hear that the problem is resolved.
    Brian - Newton Abbot, Devon, UK