    Longer pipe run splits



    Does anybody know of any 2-3kW split systems or multi-split systems that are good for a 25M piperun?

    Trying to keep costs down as our orignal quote was for 3 back to back splits. However the owner of the house has told our client that the outdoor units can't be on an exterior wall or on the roof.

    General (Fujitsu) want 3079 euros just for the outdoor unit for there multi-split system, which I'm not really a fan of, but is apparently good for a total of 60M.

    Cheers
    Paul



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Longer pipe run splits

    Hi Paul

    The total piperun of 60m is for the TOTAL connected pipe lengths - so you could have 3 indoors connected each 20m from the cond unit.

    3079 euros sounds expensive for Fuji.
    Have a look at the Daikin 4MKS90D multi split on R410a - 9kw total cooling duty with a maximum pipelength of 70m retails here Trade @ £1317 condensing unit only or the heat pump version 4MXS80D, 8kw cooling 9.6kw heating, same pipelength for £1447

    I know you can get Daikin in Spain as I've bought it there - don't know about the islands though.

  3. #3
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Longer pipe run splits

    Can extra charge be added for long runs? I know with 7kw Mitsubishi Inverta, with added charge you can run 35 - 40 meters. Taking into consideration traps and bends.....and height.

  4. #4
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19

    Re: Longer pipe run splits

    Depending on how much oil the compressor spits out, with long pipe runs and hermetic comps you risk oil starvation as the time taken to return is too long. Dunno if anyone has a suggestion for it though.
    It's a lovely day to pump some gas

  5. #5
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Longer pipe run splits

    Jesus lads
    there only splits just install them add a small amount of fridge oil additional refrigerant and walk away. If you really want to be careful fit a few oil traps.
    For **** sake just do it
    I ve fitted 3.5 kw splits with 50 mtrs on them with a small ammount of capacity drop off but they worked fine.
    T

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Longer pipe run splits

    Quote Originally Posted by techguy
    Jesus lads
    there only splits just install them add a small amount of fridge oil additional refrigerant and walk away. If you really want to be careful fit a few oil traps.
    For **** sake just do it
    I ve fitted 3.5 kw splits with 50 mtrs on them with a small ammount of capacity drop off but they worked fine.
    T
    I've also seen overlong piperuns which have caused the evaporators to start freezing with the resulting water splatter - get the right size units.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jul 2005
    Location
    UK
    Posts
    60
    Rep Power
    19

    Re: Longer pipe run splits

    Quote Originally Posted by techguy
    Jesus lads
    there only splits just install them add a small amount of fridge oil additional refrigerant and walk away. If you really want to be careful fit a few oil traps.
    For **** sake just do it
    I ve fitted 3.5 kw splits with 50 mtrs on them with a small ammount of capacity drop off but they worked fine.
    T

    Begorra!

    Whack in the gas, and scram when you've got the money!

    Do you do tarmac as well?
    .
    Sodd's the name...... Law's the game.
    Established 1791 - still going strong.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Longer pipe run splits

    Quote Originally Posted by dogma
    Can extra charge be added for long runs? I know with 7kw Mitsubishi Inverta, with added charge you can run 35 - 40 meters. Taking into consideration traps and bends.....and height.
    With most 7kw units you will find that the pipelengths are about 50m, depending on the refrigerant.

    The pipework lengths are matched to compressor power so if you put long lengths of pipework on small power comps the gas velocities are reduced thereby affecting duty and oil return.

    Similar in design to a fan - add too much ducting and the system resistance increases leaving the fan running overloaded doing very little work.

  9. #9
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: Longer pipe run splits

    Cheers lads.

    I looked at loads of makes and most of them said a max pipe length of 10-15M.

    I quoted for the daikin multi-split that Frank recommended. I think that will be ok for the client needs. I found a company in Madrid that can supply. The price was very reasonable.

    Something that does concern me though. The Daikin is almost 2500 euros cheaper than the General (fujitsu) equivelant. Whats wrong with this picture?

    If this works out OK, we will never have to touch General again. YEEHA.

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Longer pipe run splits

    Good choice.

    I think you will be impressed at how the multi works.

    The old Daikin VRV II used to tell you if it was under or over charged but the new Daikin VRV III adds the additional gas charge automatically itself to match the installed pipework lengths.

    Lots of people call the Japanese but when it comes to electronics they are hard to beat.

  11. #11
    Join Date
    Jan 2006
    Location
    Surrey
    Posts
    26
    Rep Power
    0

    Re: Longer pipe run splits

    Probably a bit late now, but Toshiba do some 25m run high-wall splits (Daiseikai II range) 2.5, 3.5 and 4.5 kW cooling capacity.

  12. #12
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: Longer pipe run splits

    I used to work mainly on Daikin when I lived in England so im happy fitting that.

    And Toshiba wash your mouth out.

    Paul

  13. #13
    rbartlett's Avatar
    rbartlett Guest

    Re: Longer pipe run splits

    does that mean you won't be coming round to do my drive??

    cheers

    richard

  14. #14
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19

    Re: Longer pipe run splits

    Good grief, it's turning into one of those threads. Who needs Marc for some random aggro?
    It's a lovely day to pump some gas

  15. #15
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19
    Blimey. For God's sake don't anybody mention anything about lepracorns
    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  16. #16
    Join Date
    Aug 2005
    Location
    Australia
    Age
    60
    Posts
    12
    Rep Power
    0

    Re: Longer pipe run splits

    Just go to the next size vapor return pipe, this will reduce the extra friction load on the compressor, and stop your liquid line icing up all the way to the evaporator.
    I have seen a few installs of long run splits (20 - 30 mtrs) that have this problem.

  17. #17
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Longer pipe run splits

    Hi Lancer. Can you elaborate further?

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Longer pipe run splits

    Just go to the next size vapor return pipe, this will reduce the extra friction load on the compressor, and stop your liquid line icing up all the way to the evaporator.
    And reduce the vapour velocity and reduce oil recovery

  19. #19
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Longer pipe run splits

    Decrease pipe size on the risers to increase velocity and therefore oil return.... Increase pipe size on the horizontals to decrease friction losses..... Both suction and liquid lines as its an heat pump....
    But could you utilise both and to what extent.... where would you meet the limit.....
    How far on average could you increase the pipe runs...
    If you are using non-standard pipe size can you still use the g/m extra refrigerant guide....

    what a tangled web we weave.............. A bit tongue in cheek i admit
    :cool: Calvo :cool:

  20. #20
    Join Date
    Aug 2005
    Location
    Australia
    Age
    60
    Posts
    12
    Rep Power
    0

    Re: Longer pipe run splits

    Hi Lancer. Can you elaborate further?
    hybridjunction,
    hi hows things?, in my experiences I have found that most split have a metering device (capillary tube) at the compressor end before the liquid line service valve, so depending on the system balance (liquid/vapor) when the delivery head is to high, there is a tendency for the suction pressure to drop to low across the evaporator/distributor causing the liquid to boil off back down the line. Depending on the charge (to some degree) I have seen units with the armaflex on the liquid line sweating from the head to the compressor, I can only assume that armaflex has been pushed past its insulation value (-10 deg C) by the excessive run length and insufficient gas.

    And reduce the vapor velocity and reduce oil recovery
    Frank hi,
    your point is very valid and should always be taken into consideration when working with installs where the head is located below the compressor, most manufactures recommend P traps in this situation. In the other case where the compressor is below the head I have found that gravity is sufficient to return enough oil for the compressor to operation normally.

    I am interested in the views of others upon this subject because I am frequently confronted with installs where the client wants the condenser positioned past the recommend pipe length.

    On an other point, how many guys look at the super heats across the evaporator; or just use the sub cooled vapor pressure, to determine correct charge? I have often wondered how may splits have had there efficiency affected by under or overcharge condition caused by pipe length.

    Please forgive me if this subject has been bashed about this forum before, I must admit it is a pretty obvious problem with pre-charged units.

    Lance.

  21. #21
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Longer pipe run splits

    Hi Lancer. Things are good u?

    By increasing suction pipe size does this not "raise" evap pressure giving better efficency? Assuming the pipe lenght is the same as it would have been with the smaller dia.

  22. #22
    Join Date
    Aug 2005
    Location
    Australia
    Age
    60
    Posts
    12
    Rep Power
    0

    Re: Longer pipe run splits

    hybridjunction

    By increasing suction pipe size does this not "raise" evap pressure giving better efficiency? Assuming the pipe length is the same as it would have been with the smaller dia.
    Yes my thoughts exactly, I have use this principal successfully on many installs.

    Lance

  23. #23
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: Longer pipe run splits

    It's a bit late now because I no longer need a unit capable for a long, but I found one!!

    The Toshiba R410A Daiseikai Inverter Split system are good for 25M. They come pre-charged for 15M.

    Just thought I'd post this for future reference.

    Paul..

  24. #24
    Join Date
    Jan 2006
    Location
    Surrey
    Posts
    26
    Rep Power
    0

    Re: Longer pipe run splits

    It's a bit late now because I no longer need a unit capable for a long, but I found one!!

    The Toshiba R410A Daiseikai Inverter Split system are good for 25M. They come pre-charged for 15M.

    Just thought I'd post this for future reference.

    Paul..
    Errr, didn't I mention that on page 2 of this thread?

    You told me to wash my mouth out, which I did.

  25. #25
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: Longer pipe run splits

    oh yeah. Errrm. I'll go and find the soap. Sorry.

    Actually I'm thinking about giving Toshiba another go. I used to look after a site in Bradford that had loads of Toshiba splits and VRF's and they were always breaking. We use to get a couple of call outs a week there, hence why I dislike Toshiba. However, from what I have read recently, it might not actually be bad kit.

    I need to find someone who does a decent cassette, single blow and ducted system. I'm fed up with installing General.

    So, if Toshiba ever get back to me and tell where I can buy it, I might give it a go. Alternatively im also looking at Hitachi and Mitsi-elec.

    Regards (and sorry, again)

    Paul..
    Last edited by airefresco; 01-03-2006 at 03:22 PM.

Similar Threads

  1. Pipe runs
    By SPR in forum Air Conditioning
    Replies: 11
    Last Post: 07-04-2009, 07:28 PM
  2. pipe sizeing tool
    By Latte in forum Tools and Calculators
    Replies: 5
    Last Post: 10-12-2003, 11:32 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •