    Evaporator Fin spacing Defrost
    could someone point me in the right direction, regarding evaporator defrosting, mainly the fin spacing and effect on the defrost.
    correct me if im wrong
    the smaller the fin spacing, equals the more fins per inch, resulting in a greater surface area, and making frost build up easier due to the smaller gaps between the fins.
    as a result the defrost period would have to be increased and the interval more often, the the same size evap with a bigger fin spacing and less fins per inch
    Oct 2007
    manchester
    44
    5,707
    Re: Evaporator Fin spacing Defrost
    fridge or freezer??
    Jun 2009
    North East England
    35
    714
    13
    Both........
    Oct 2007
    manchester
    44
    5,707
    any fridge should have off cycle defrost by either 3 deg deadband on the stat to defrost an evap or if fanned then again- anything over a 2 deg diff would be sufficient, sometimes a 4x20 min defrosts with just fan will cure it, for a freezer at -18 then again 4 defrosts for upto 40 mins with electric defrosts with a termination stat setpoint of 25deg and a 2 min fan delay or 2 min dripping time
    Jun 2009
    North East England
    35
    714
    13
    That's true, but what considerations should be made with different fin spacing with regards to defrosting
    Oct 2007
    manchester
    44
    5,707
    you havent given us much details into the application, do you want a manual???
    Jun 2009
    North East England
    35
    714
    13
    This is just a generalisation, regrading fun spacing and defrost, I'm good for manuals
    Oct 2007
    manchester
    44
    5,707
    Oct 2007
    manchester
    44
    5,707
    Jun 2009
    North East England
    35
    714
    13
    gotta share the love
    Feb 2013
    Rochester, NY
    38
    Tighter fin spacing is going to make defrost more frequent because you'll obstruct airflow faster. Depending on the defrost method, defrost duration could be shorter.
    Iceman717
    Compressors in the basement, condensers on the roof, evaporators everywhere else. :cool:
    Dec 2010
    Toronto, Canada
    54
    1,492
    My local mentor designs his coils with 10-12fpi, more packed than that wastes defrost energy but I can see why the japanese pack them in, way less manufacturing/shipping costs