    Is it possibel to have room pressurized with no fresh air intake?



    Hi,

    This may sound weird, last week one of my clients was arguing with me, with the fresh air dampers closed, and just by recirculating the air (AHU blower), it is possible to pressurise the room. He was confused with the "extrernal static" developed by the AHU fan is suffuciet for pressurising the room.

    How can I make him understand that this is not possible? Any justifications is much appreciated.

    Thank you
    Nevin.



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Is it possibel to have room pressurized with no fresh air intake?

    where is he going to magic up this additional pressure - from thin air??

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Is it possibel to have room pressurized with no fresh air intake?

    Quote Originally Posted by r.bartlett View Post
    where is he going to magic up this additional pressure - from thin air??
    Now that is being down right sensible and you should know right
    now that customers are vary rarely sensible.....



    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Is it possibel to have room pressurized with no fresh air intake?

    Although not very sensible it can be done LOL

    Just make the return air plenum a lot bigger than the room and size your room size not much bigger than the supply duct.

    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Is it possibel to have room pressurized with no fresh air intake?

    It's very simple really.

    The room, sealed, contains a fixed amount of air at a fixed pressure, atmospheric.

    Fit an extract duct inlet to the room and then fit that duct onto a fan which has a supply duct outlet also connected to the room. With this layout the room, ducts and fan are now a complete sealed space. Assume that both ducts are of identical size and shape.

    Turn on the fan an it will create a negative pressure on the inlet duct to enable it to withdraw air from the room. Now nature abhors a vacuum so in an attempt to replace the air withdrawn by the fan from the room nature accepts the air being blown out by the fan supply duct and the room remains at atmospheric pressure.

    Assuming some numbers...

    Extract duct resistance is 200Pa, supply duct resistance 200pa.

    For the fan to move any air it needs to be able to suck at 200Pa and blow at 200Pa so need to be rated at 400Pa, there is no extra supply pressure within the circuit to pressurise the room.

    Tell him to read this..
    http://www.google.co.uk/url?sa=t&rct...42965579,d.d2k
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: Is it possibel to have room pressurized with no fresh air intake?

    Thank a lot... Brain... After all customer is the King, even if he is an idiot!

  7. #7
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Is it possibel to have room pressurized with no fresh air intake?

    Don't need a fresh air intake. Just a compressed air line.....

  8. #8
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: Is it possibel to have room pressurized with no fresh air intake?

    Quote Originally Posted by sterl View Post
    Don't need a fresh air intake. Just a compressed air line.....
    Storing air in cylinders? How should be the calculations?
    Last edited by Brian_UK; 03-03-2013 at 03:01 PM.