    Mar 2012
    United Kingdom
    42
    63
    13
    Thumbs up Low oil pressure CARRIER 30 XA
    Hi guys sorry to bother but I am really desperate what to do with one Carrier water chiller 30 XA Carlyle screw compressor . . .
    Low oil pressure indicate on controller the old one not that new ( slow ) .
    Found on oil pressure transducer trace of oil and lose transducer and was leaking but very very slow .
    I changed transducer but after while again the same fault .
    What should to do next and make sure is just missing oil from compressor ...
    Thanks for any advice .
    Have nice Evening
    P.S Can I just top it up or replace all oil ... ???
    Somerset
    69
    4,698
    Re: Low oil pressure CARRIER 30 XA
    Hi.
    Have you considered the fact that the oil filter may need replaceing?
    Jun 2009
    North East England
    41
    712
    Hi.
    Far too easy that, in fact the oil filter is the easiest filter in the world to change
    Mar 2012
    United Kingdom
    42
    63
    13
    How to confirm is definitely just OIL Filter ... ? D
    Mar 2012
    United Kingdom
    42
    63
    13
    sort it thanks
    Feb 2008
    Sudan
    89
    Check the difference between the discharge pressure & oil pressure, should not exceed 50 psi.
    Apr 2009
    israel
    778
    how long after start up do you get this fault?
    check on the prodialog screen oil level input , this will give you some indication what your problem is .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!