Thread: Low oil pressure CARRIER 30 XA
26-02-2013, 08:21 PM #1
Hi guys sorry to bother but I am really desperate what to do with one Carrier water chiller 30 XA Carlyle screw compressor . . .
Low oil pressure indicate on controller the old one not that new ( slow ) .
Found on oil pressure transducer trace of oil and lose transducer and was leaking but very very slow .
I changed transducer but after while again the same fault .
What should to do next and make sure is just missing oil from compressor ...
Thanks for any advice .
Have nice Evening
P.S Can I just top it up or replace all oil ... ???
26-02-2013, 08:39 PM #2
Re: Low oil pressure CARRIER 30 XA
Hi.
Have you considered the fact that the oil filter may need replaceing?
26-02-2013, 10:36 PM #3
27-02-2013, 07:43 AM #4
How to confirm is definitely just OIL Filter ... ? D
28-02-2013, 05:17 PM #5
sort it thanks
05-06-2013, 06:12 AM #6
Check the difference between the discharge pressure & oil pressure, should not exceed 50 psi.
05-06-2013, 01:10 PM #7
how long after start up do you get this fault?
check on the prodialog screen oil level input , this will give you some indication what your problem is .
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!