Re: once more about oversized evaporator
Something else to beware of is oil return. There might be excessive oil in the coils due to reduced flow. Oversizing a condenser is much less likely to cause problems since the condensing refrigerant makes a good solvent.
-
27-08-2013, 09:49 AM #2
Re: once more about oversized evaporator
NiHaoMike mentioned:
Something else to beware of is oil return. There might be excessive oil in the coils due to reduced flow. Oversizing a condenser is much less likely to cause problems since the condensing refrigerant makes a good solvent.
Amazing the small things we often miss in a design, or retrofit.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )