    Re: once more about oversized evaporator

    Something else to beware of is oil return. There might be excessive oil in the coils due to reduced flow. Oversizing a condenser is much less likely to cause problems since the condensing refrigerant makes a good solvent.

  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: once more about oversized evaporator

    NiHaoMike mentioned:
    Something else to beware of is oil return. There might be excessive oil in the coils due to reduced flow. Oversizing a condenser is much less likely to cause problems since the condensing refrigerant makes a good solvent.
    A very interesting point. Good one. I'd imagine the evap circuiting would also need to be set up to minimise oil entrapment.

    Amazing the small things we often miss in a design, or retrofit.