    Anyone had any problems with two way heat pump driers failing, specificaly the check valve breaking up and blocking the drier in one direction of flow?
    Any manufacturers you would recommend or avoid?
    Jun 2009
    Lusk , Dublin
    1,115
    Re: Heatpump drier failures...
    Drier manufacturers or heat pump manufacturers???
    If it's drier's Danfoss DMB range
    If it's heatpumps depends on the application
    Stu
    Tool's ? check ! Condom's ? check !
    3,853
    Sporlan two way driers, HH165's
    The original Alco ones were ok, wish i hadn't changed them now!
    Jun 2009
    Lusk , Dublin
    1,115
    Sporlan are usually OK can only recall one failing and that was a long time ago.
    Try to stick to Danfoss mainly as I don't have to pay the bill.
    Not a fan of Alco at all could tell a few horror stories about thier stuff.
    Stu
    Dec 2010
    Toronto, Canada
    1,454
    You guys aren't talking domestics I expect....
    3,853
    Quote Originally Posted by MikeHolm View Post
    Its on a big daikin thing, 8 cylinder comp think its about 80kw, has two driers as coil split in two circuits.
    Dec 2010
    Toronto, Canada
    1,454
    Thought not...
    Auckland
    74
    3,357
    38
    Bi-flow driers on a 80kw system seems like a cheap option, from memory the sporlans have a sprung loaded internal bypass if differential gets too high, could be totaly wrong though. I prefer Sporlan.