    RS CK6-D gas powered valve issues



    We just installed 12 of the RS CK6-D dual position gas powered valves, these valves have two pilots, both energized= valve closed, both de-energized = valve open Parker says pilot #1 off and #2 on = bleed. This doesn't work, its backwards the way I see it. It's like Parker has their literature wrong, or the valve is stamped wrong. Anyone using this valve? Any input?



  2. #2
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: RS CK6-D gas powered valve issues

    Hi Jason
    We have started using CK-2D valves which are basically the same valve I think. With the CK-2D the valve is open when both are de-energized and shut when both are energized, for bleed coil 1 is de-energized and coil 2 is energizer. This is how we have wired them up and they seem to work fine.
    From the paperwork we have coil 1 operates on the main piston and coil 2 operates on the small or secondary piston. When you leave coil 2 energized and de-energize coil 1 the main piston can only open as far as the small or secondary piston allows.
    Hope this makes sense.
    Regards
    Paul

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: RS CK6-D gas powered valve issues

    You should have a regulation pilot somewhere on the RS valve, solenoid pilots are just that either open or closed. Seems odd to have two solenoid pilots. Energized pilot means fully open, de-energized means regulation on second regulatable pilot. Check the Hantech site for clarification of operation of base vav

  4. #4
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: RS CK6-D gas powered valve issues

    Go to Parker's site and search CK-2D or CK-6d Parker Literature

  5. #5
    Join Date
    Feb 2013
    Location
    USA
    Age
    46
    Posts
    2
    Rep Power
    0

    Re: RS CK6-D gas powered valve issues

    Quote Originally Posted by PaulZ View Post
    Go to Parker's site and search CK-2D or CK-6d Parker Literature
    I checked the site and spoke with Parker, couldn't get a straight answer out of them, they seemed to think they may have problems with their literature. Still awaiting a reply?

  6. #6
    Join Date
    Feb 2013
    Location
    Rochester, NY
    Posts
    38
    Rep Power
    0

    Re: RS CK6-D gas powered valve issues

    Switch it and see what happens? I recall sometime ago R/S changed one of their valves so that it took the opposite control to achieve the result. Man, the cobwebs in my head... I'm kind of thinking it was the A4AD though.
    Iceman717

    ---
    Compressors in the basement, condensers on the roof, evaporators everywhere else. :cool: