Results 1 to 3 of 3
  1. #1
    Join Date
    Aug 2011
    Location
    Uk
    Posts
    48
    Rep Power
    0

    Lightbulb Mitsubishi electric PURY-EP300YHM-A Fuse F4



    Hello there,

    I have a problem with a pury-300. Fuse was blown on the noise filter board F4. I was informed by the Mitsubishi that this fuse supplied the M-Net board. After removing the board and seeing that there was a big flash burn behind the capacitor we decided it was a problem with the M-Net board. It has taken about 3 weeks for delivery of the new board. I replaced the fuse and board today only to turn it on and the fuse to blow straight awy. This also knocks out the 20A fuse on the distribution board supplying power to L2.

    Any Ideas?

    Thanks in advance




  2. #2
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi electric PURY-EP300YHM-A Fuse F4

    You have a tester, there are schemes of payments, ring out and find out where short circuit.

  3. #3
    Join Date
    Aug 2011
    Location
    Uk
    Posts
    48
    Rep Power
    0

    Re: Mitsubishi electric PURY-EP300YHM-A Fuse F4

    Noise filter board screwed.
    Tried it with board from the slave unit. All good. New board in the post,


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •