    Supply and Extract Calculator



    Hi Guys and Gals

    Just wondering if anyone has a easy way of working out what size extract or supply fan i would need for a certain area. i.e. if i take the room measurements how should i calculate it? it has always been something someone else has done. Any help will be appreciated

    Lee



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Supply and Extract Calculator

    Let us have the room details and also indicate the proposed use of the area as the ventilation rate is dictated by the application.
    Location, United Kingdom

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Supply and Extract Calculator

    You need to know the type of room occupancy from which you will be able to find the number of air changes per hour. A simple calculation from there on.

    Or, with the power of our friend Google....

    http://www.tlc-direct.co.uk/Technica...tilation4.html
    Last edited by Brian_UK; 18-02-2013 at 10:12 PM. Reason: Added link
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Supply and Extract Calculator

    The room is a Lab 3.5m x 5.3m x 3m high there is a fume extraction in place doing 4,000m3 per hour they need a simple supply to make up for the extraction

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Supply and Extract Calculator

    I think that you have part of your answer within your own statement.

    If the fume cupboard is running then they need something to replace the extracted air. If it's not running full time then perhaps some form of speed control is needed.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Supply and Extract Calculator

    Thanks for the help people

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Supply and Extract Calculator

    A static duct from external of structure will assist fume cupboard extract. 4000 m3 / hr is 1100 plus litres per second. Which would create a semi negative pressure in area without static make up air, could have been an initial design requirement to reduce contamination in localized area.