    Angry Daikin vrv L series !!!



    Hi guys , has anyone else had this problem with L series vrvs that are daisy chained together .... Yesterday I had to take one fan coil off a system to fix so as to leave rest of system operational , do when I done a hard reset on outdoor unit , all other systems in this compound that are daisy chained back to I controller went into fault , I basically had to spend hours doing a full comms reset on each unit !!! Bloody nightmare , I have only ever had this problem with the daikin vrv L series !!

    Anyone else had the Same prob ???



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin vrv L series !!!

    you would have to do a full reset on the outdoor so it cannot find the unit u removed- also the indoor address would req deleting off the i controller- diversity wouldnt be an issue- i got a vrv2 with a noisy indoor fan - replaced fan and capacitor- runs ok until after 20 mins and its noisy as fook- swapped indoor pcb with another unit - other unit ran ok, for 30 mins- but i controller alarmed like fook on comms error as addresses wrong- so indoor fan motor is ok as it runs for 20 mins ok, daikin dont usually send out duff kit- tehnical said test voltage n-e 0v l-e 245 l-n 245 when its ok and when its noisy- it aint catching on the cowl- 145quid for another fan if its tested ok ??

  3. #3
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Daikin vrv L series !!!

    Didnt have to deleat address from I controller, it just buggered sllbthebother systems when I done the hard reset to get this one fcu off line ..