    Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster



    hi how's everybody , i had installed four set Daikin VRVIII RXYQ240PTJU ( RXYQ120PTJU +RXYQ120PTJU) from the master condenser ,the hot gas solenoid valve blasted with malfunction code E3 , replace with new part solenoid valve ,coil,and the filter . Three week later ,blaster again the same part with the code E4. Do someone can help me in the case coz i need to reorder the those part again to make it run in heating mode . it already wasted 85 lbs gas R410 ....i call the Daikin tech support , their said their never met this problem before ..... Thank you so much



  2. #2
    Join Date
    Feb 2013
    Location
    New York
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster

    blaster = pipe exploded

  3. #3
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster

    which make solenoid valve did you use? I hope it should be compatible with R410A pressures. what was the discharge pressure you observe?

  4. #4
    Join Date
    Feb 2013
    Location
    New York
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster

    i'm order those part from the dealer and i'm sure that was the 100% same as the original , when high pressure ,then high pressure switch should cut off the system .... but it not ....

  5. #5
    Join Date
    Feb 2013
    Location
    New York
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster

    when in heating the pressure was around 145psi and 420 psi

  6. #6
    Join Date
    Feb 2013
    Location
    New York
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster


  7. #7
    Join Date
    Jan 2012
    Location
    usa
    Age
    44
    Posts
    2
    Rep Power
    0

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster

    finally the problem is fix , that was the inverter compressor wasn't compressing so well ,sound so loud and vibration too much to cause the pipe explored . when i replace the part in second time , the error code for the inverter compressor coming out . so after replace the new compressor everything running like new before

  8. #8
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Daikin VRVIII outdoor condenser , the hot gas solenoid valve blaster

    Since the launch of the equipment how much time passed?