Results 1 to 2 of 2

Thread: A few basics...

  1. #1
    Join Date
    Jan 2013
    Location
    Australia
    Posts
    2
    Rep Power
    0

    A few basics...



    Hi,
    im new to the trade and understand that for an A/C system at least a 10 degree C TD on indoor and outdoor coil's is an indication of normal operation and 4-8k degrees C subcool and 4-7k superheat.
    What are the values for medium and low temps?
    Thanks for any help



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: A few basics...

    .

    For most systems you'll get by with the same figures.

    In the UK we work to about 15 Degs difference over the cond (outside unit)
    but that is just splitting hairs.

    When you stop working to rules of thumb and start being exact,
    the 10 degree rule is not as accurate, especially if you are
    working on things like fresh meat. Because a wide Delta T (temp difference)
    over the evaporator tends to dry out the meat too much and ruin it,
    with fresh meat you might have a Delta T of 2 degs.

    In essence your figures are what we use give or take and for the most
    part, that will hold true for most types of system, whether low temp, medium or high.

    Regards

    Rob

    .
    Last edited by Rob White; 12-02-2013 at 05:31 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..