    marshal heat pump split defrost problem



    hi
    i have marshal 2 ton split unit r22
    in heating mode it work perfectly
    the outdoor fan never stop working
    then discharge temp is 110 c
    suction is 55 c
    13 amp current

    compressor is not hot
    i set indoor unit to 32 c
    but the outoodr fan never stop spinning
    and water is continue flow from outdoor unit
    i suspect the indoor sensor on pipes may be not fixed correctly so i unpluged it then plugged it
    so the outdoor fan stopped work and compressor kept running
    after one day
    i turned on the split so
    the fan and compressor kept working never stoped until the room temp is reached 32 c
    so both comp and fan stopped
    so what the cause of the problem
    Last edited by kefah; 11-02-2013 at 03:09 PM.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: marshal heat pump split defrost problem

    "discharge temp is 110 c" but "compressor is not hot"???

    With a suction temp of 55ºC and a discharge of 110ºC I would expect the compressor to be hot as well...

    Although it would be nice to know the pressures this machine is operating at I feel that the first thing to do, considering the high temperatures, is to reclaim the refrigerant and see if it is short of charge.

    Another thing that might give similar symptoms is if there is a problem with the reversing valve but I would start with checking the charge.

    Happy hunting.



    .

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: marshal heat pump split defrost problem

    thank u
    sorry for mistake
    55 c is not the suction temp
    its the indoor unit return temp

  4. #4
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: marshal heat pump split defrost problem

    the discharge pressure is beween 250 and 325 psi

  5. #5
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: marshal heat pump split defrost problem

    the problem is solved
    out door fan didnt stop because the temperature in indoorunit was not reached the required temp to make the outdoor fan stop
    thank u all