    Howdy from Texas. Well, looks like the US is opening up limited use of HC R290 and R600a.
    I would really appreciate some advice/info from you guys on best practices, types of
    service equipment/tools you use in the service of this equipment. Recovery, Evacuation,
    Service connections etc. I know you are well ahead of the curve on these refrigerants
    and am hoping to glean as much info as possible. Any help, Info, In-sight would be greatly
    appreciated. Many Thanks,

    GF



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Texas Seeking Info on HC Refrigerants


  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Texas Seeking Info on HC Refrigerants

    In general they are just like any other refrigerant in the need for safe and careful handling.

    The recovery machine obviously needs to be suitable for HC use. Another tool which is semi-critical is having a combustible gas leak detector operating near you when you are breaking into a system for any reason. The type used by a gas fitter is quite good enough.

    If working on a system always recovery and then purge through with nitrogen before any brazing work.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2006
    Location
    West Texas, U.S.A.
    Age
    75
    Posts
    17
    Rep Power
    0

    Re: Texas Seeking Info on HC Refrigerants

    Thanks for the replies. So I would assume that due to the small
    quantity of refrigerant in the systems, an empty cylinder with a
    deep vacuum would be suitable for recovery. Nitrogen purge, make
    what repairs were required, evacuate and recharge?

    It is my understanding that the service ports shall be of a different type.
    I assume maybe left hand, smaller, larger etc. Is that the case over there?

    Do you know of a recovery machine that is approved? Make model etc would
    be appreciated. Not finding much on mfg data here. May not be looking in the
    right place.

    Do you find most troubleshooting to be done with Temp diagnostics? I would
    assume as with any machine, hosing up is a last resort?

    Again, Many Thanks.........GF

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Texas Seeking Info on HC Refrigerants

    Haven't found any difference in service port sizes, usual 1/4 flare hose connectors. Rest of your comments are good.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Nov 2006
    Location
    West Texas, U.S.A.
    Age
    75
    Posts
    17
    Rep Power
    0

    Re: Texas Seeking Info on HC Refrigerants

    Thanks for the input, I really appreciate it.........GF

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Texas Seeking Info on HC Refrigerants

    .

    The difference with HC refrigerants as apposed to the others (in the UK anyway)
    is we are allowed to vent it to atmosphere.

    It has to be done in a controlled manner and there are limits to this but because
    of the low GWP, we can vent it.

    On a Data sheet from one manufacturer they recommend disposal as flaring it off.
    Burning it in other words and I have a propane Bunsen-burner and demonstrate this
    to students by connecting it up to the fridge and burning the gas(**).

    The biggest worry with the gas is the electrics. Normal electrics with switches may
    not be suitable for HC refrigerants unless they are removed up and out of the way
    of the gas or are inside sealed units to prevent gas ingress. If the electrics are to be
    potentially in the gas then they tend to be solid state..


    (**needless to say there are severe safety implications to this and flash back arresters,
    correct equipment and full risk assessments have been carried out first.
    Do not do this without full risk assessment beforehand, in fact DON'T ever do it
    and never say Rob told you ).

    Regards

    Rob

    .
    Last edited by Rob White; 12-02-2013 at 05:02 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Texas Seeking Info on HC Refrigerants

    Yes like Rob says don't do it. But if you do, connect your hoses to a purging stack/bunsen burner, and set your guage pressure to 0.55 psi and make sure you do it outside!
    Training may be finished but experience is never complete.