Results 1 to 9 of 9
    Oct 2008
    newbury
    1,444
    37
    vav and balancing
    Chaps
    have we any air balancing experts here??
    Got asked to tender some air balancing and verification prior to a refit. The total air needs confirming and each unit tested. The site has 25 VAV units as per pic.
    How long would you expect to spend both in money and time as I have to give approx by this weekend :-(
    Oct 2007
    manchester
    5,639
    45
    Re: vav and balancing
    you have to allow for leaks in ductwork, and bodges where theres open ducts in the roof space, also the ahu will be operating on a supply air pressure transducer and inverter so you would have to fix the supply fan to give a fixed output and ur vav 's are adjusted off a maximum/minimum regulatin valve, you will find tubes popped off and if the system does heating, the bellows cook and air rattles through as the bellows wont deflate properly
    http://www.mediafire.com/view/?6y54s03g5gbzc4g
    Oct 2008
    newbury
    1,444
    37
    Great stuff but I need budgets. I was thinking 1/2 hr per VAV box + 2 days for the system. It all looks old and tired though...
    Oct 2007
    manchester
    5,639
    45
    and the rest, as you will need to recheck them, also ceiling tiles should be refitted as usually ur return air is ur void
    Oct 2008
    newbury
    1,444
    37
    Quote Originally Posted by install monkey View Post
    Ok will double my estimate and see what they say :-)
    Aug 2007
    Sydney
    52
    1,083
    23
    From my limited experience of once on same type of job but bigger I would allow 1.5 days for the vavs and 1/2 day for the ahu with two guys of course = 4 days, plus 1/2 day to write report and present spread sheet then add a day for the safety factor.
    AHU need to measure with fan at 100% with all vavs 100%, 100% return, then 100% fresh, both filter and coil velocities and area for calculation. Normally expect 10% leakage. Measure static at index (last box), fan statics, plenum statics, fan r/m etc.
    Oct 2008
    newbury
    1,444
    37
    Quote Originally Posted by Tesla View Post
    that works out roughly what i allowed so my guess is reasonable - bet my price won't be ;-)
    Oct 2007
    manchester
    5,639
    45
    11,024
    Looks like a nice leaky pneumatic system to play with, have fun with it.