    Defrost interval in Daikin RXS35G -series.



    Hi!

    Is it possible to make longer defrost interval at Daikin RXS35G series heatpump?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Defrost interval in Daikin RXS35G -series.

    Defrosting is carried out by the cooling cycle (reverse cycle). The defrosting time or outdoor
    heat exchanger temperature must be more than its fixed value when finishing.
    Detail Conditions for Starting Defrost
    The starting conditions must be made with the outdoor air temperature and heat exchanger
    temperature. Under the conditions that the system is in heating operation, 6 minutes after the
    compressor is started and more than 28 minutes (20/25/35 class), 30 minutes (42 class), or 44
    minutes (50 class) of accumulated time pass since the start of the operation or ending the
    defrosting.
    Conditions for Canceling Defrost
    The judgment must be made with heat exchanger temperature.
    (20/25/35 class : 4°C-22°C, 42 class : 4°C-15°C, 50 class : 4°C-12°C)