Results 1 to 24 of 24
Thread: Vrv2 pumdown
-
08-02-2013, 02:04 PM #1
Vrv2 pumdown
Hi can anyone tell me the procedure of pumping down a daikin 3 pipe vrv 2 , need to install a bs box and don't want to waste time reclaiming gas ??
And how do I know that someone has responded , I'm new to this site today ??
-
08-02-2013, 06:33 PM #2
Re: Vrv2 pumdown
best to degas it so you can compare to the stated total system charge- most vrv's have additional charge so you will struggle to get it in the condenser and also if outdoor valves pass, you could be putting nitrogen into the circuit or losing gas whilst u modify the system.
just get a 50kg reclaim bottle and degas whilst ur mounting ur bs box,running comms and piping
dont forget to drive valves open in setting mode 2 on the outdoor
-
08-02-2013, 06:58 PM #3
Re: Vrv2 pumdown
It's already got all the comms etc , just that this one bs box is knackered and I have to put new one in , I'm sure the charge is ok , usually I would degas everything but my knobhead boss cut the time on job on quote , and has told me to pump down ??
-
08-02-2013, 07:05 PM #4
Re: Vrv2 pumdown
Sorry forgot to say it's an exsiting system in a hotel , also does anyone know the pipe sizes on the bs box bsvq100mav1 , will I need fittings or will it be ok to just braze out the pipe work and fit the new box to exsiting pipe work ??
-
08-02-2013, 07:09 PM #5
Re: Vrv2 pumdown
vrv2 bs boxes are all flare connections
-
08-02-2013, 07:15 PM #6
Re: Vrv2 pumdown
It's a 410a system , these are brazed ..
-
08-02-2013, 07:16 PM #7
Re: Vrv2 pumdown
Wish it was flare connections . As the position where it is in corridor is s nightmare to get to
-
08-02-2013, 07:22 PM #8
Re: Vrv2 pumdown
haha- we did a vrv2 5yr ago, all bs boxes flared, did hear that vrv3 was sweat connections- trying to find details for ya
-
08-02-2013, 07:38 PM #9
Re: Vrv2 pumdown
http://www.mediafire.com/view/?zycv21zhkxx6l1f
pg 15 has bs pipesizes
-
08-02-2013, 07:40 PM #10
Re: Vrv2 pumdown
Cheers mate !!
-
08-02-2013, 07:50 PM #11
Re: Vrv2 pumdown
best way is to hacksaw the pipework at the bs box- remove the swarf from the pipework, unsweat the stubbs, bish bash bosh- access permitted
-
08-02-2013, 07:54 PM #12
Re: Vrv2 pumdown
Yep , that's what I was thinking ,, but getting to this box is a headache , what with all the other **** around it.. I should crack it tho
-
08-02-2013, 08:09 PM #13
Re: Vrv2 pumdown
http://www.advancedengineering.co.uk...data_sheet.pdf
other similar products are available, i do not profit or benefit in any way by showing this link!!
-
08-02-2013, 08:42 PM #14
Re: Vrv2 pumdown
I could do with some of that !! Heat mat will have to do now
-
08-02-2013, 09:09 PM #15
Re: Vrv2 pumdown
good for squirting at apprentices knackers-has a good range too
-
08-02-2013, 09:48 PM #16
Re: Vrv2 pumdown
http://www.mediafire.com/view/?82uk7ar76kn32n5
no reference to pumping down
-
08-02-2013, 09:50 PM #17
Re: Vrv2 pumdown
When u said drive valves open when reclaiming gas , do you mean the setting 21 on pcb ??
-
08-02-2013, 09:54 PM #18
Re: Vrv2 pumdown
yep thats it- use it for reclaiming excess charge and pressure testing and vaccing and also for dumping gas in when charging too
-
09-02-2013, 10:28 AM #19
Hi Darrenp welcome to RE forum.
There's simple thing you can do.
Set the whole system to cooling mode 16°C; set point unit OFF
Then after run under mode 2 code six binary set 1 (forced demand)
Wait til you feel your outdoor reach his max value and then stabilized ( or see your service checker, or wait for example 20 mn and verify the rooms are cold enough).
Then after push once the MODE button on outdoor main pcb to stop the forced mode.
At this time the VRV will recover the maximum gas as a pump down.
Be careful that nobody will start the system.
Close the 3 valves (or more in multi combination and in this case be careful of oil egalisation too)
Set mode 2 code 21 binary set 1 (EEV opening)
Then recover the gas... I don't know exactly your system but i think you'll recover from 0.5 to 1 kg ( i hope so!! )
Kind regards
Cool#9
Sent from my Nexus 7 using Forum RunnerLast edited by cool#9; 09-02-2013 at 10:47 AM.
-
09-02-2013, 02:32 PM #20
Re: Vrv2 pumdown
Cheers cool 9 , but what is this code exactly ,, I know the 21 code to open all valves , what's the other one your talking about and the procedure ???
-
09-02-2013, 02:33 PM #21
Re: Vrv2 pumdown
Set point unit OFF ?? Could you explain further please
-
09-02-2013, 03:00 PM #22
Re: Vrv2 pumdown
Hi
The other one allows you to drive all indoor units in "TEST" mode manualy in cooling or heating (even fan only if you need ) let's call it "forced operation"
It' s quite useful don't need to set each remote control to this function, just do it once from your VRV.
Then after when you leave the customer settings remain the same...
After, by "unit OFF" mode i just mean to stop the unit by the remote control.
rgds
cool#9
-
09-02-2013, 03:27 PM #23
Re: Vrv2 pumdown
Ok but what way do I do it on pcb !?
-
10-02-2013, 03:24 PM #24
Re: Vrv2 pumdown
Service Manual VRV2 Heat Recovery Si39306.zipHello Darrenp
Just take a look at the attachement it's a sample of service manual, print it and go on sight with it.
Have a gook luck.
Kind regards
cool#9