    Daikin inverters



    Hi all I hope someone can assist me with this one. I have been too a few calls in the last year where the customer is complaining their air conditioning is not working in cooling( these specific calls are all daikin split systems). And when I arrive the units seem to be working. After a few minuets the units stop cooling, the fan is still running on the indoor but the compressor has shut down and then the fans. No fault code is shown. Then after about the same around of time the units start cooling again. Their is more than enough load in the rooms and it is set to cooling, but the units just don't seem to want to run. Any ideas will be much appreciated



  2. #2
    Join Date
    Mar 2005
    Location
    Birmingham U.K.
    Age
    70
    Posts
    54
    Rep Power
    20

    Re: Daikin inverters

    Hi Bigspee
    Sound like the systems are cycling on the freeze protection sensor on the evap coil. If the coil reaches below,(I think -6c) the cooling compressor stops running until the coil warms up and then the cooling will restart after the anti cycle timer run out.

    You need to monitor the sensor temperatures from the remote controller.

    If the unit is cycling on the freeze protection it is usually due to the system being s.o.g !

    regards

    Bob

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin inverters

    Model numbers might help

  4. #4
    Join Date
    Aug 2005
    Location
    uk
    Age
    46
    Posts
    82
    Rep Power
    19

    Re: Daikin inverters

    Comms rooms by any chance??

  5. #5
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Daikin inverters

    Various models all doing the same thing

  6. #6
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Daikin inverters

    And 3 of them in comms rooms

  7. #7
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Daikin inverters

    And thanks bob

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •