I'm a newbie trying to understand the HVAC system. My query is on what parameter is the evaporator temperature fixed? What would be its value for room air conditioning, chiller, freezer etc? I'm trying to select a electrical compressor for a cooling load of about 0.8 ton.
-
07-02-2013, 04:26 PM #2
Re: Evaporator temperature value
general rule of thumb, is your evaporating pressure / saturated temperature is 10k below your required space temperature
R's chillermanIf the World did not Suck, We would all fall off !
-
08-02-2013, 05:08 AM #3
Re: Evaporator temperature value
I have a compressor datasheet. Its details are as follows..
Capture.jpg
My cooling capacity is around 2500 Watts. My required temp is 25deg celsius. To use this compressor, I have to run it with rpm in between 2800 and 3700 rpm. The corresponding evap temp is 10deg celsius. Is this deduction correct or am I looking at a mismatched compressor?
-
08-02-2013, 07:33 AM #4
Re: Evaporator temperature value
Hi princejoy
That is a question different from the first. The compressor is med to hi temp and will do the job at 3700 but struggle towards 2800. So go for a bigger compressor. What rpm will you be using - fixed on voltage supply?
Did you mean you cooling load as opposed to cooling capacity?
-
11-02-2013, 04:27 AM #5
Re: Evaporator temperature value
-
11-02-2013, 04:29 AM #6
Re: Evaporator temperature value
I can also run the compressor at any desired speed with a constant voltage supply.(depends on the control circuit modification).