    I'm a newbie trying to understand the HVAC system. My query is on what parameter is the evaporator temperature fixed? What would be its value for room air conditioning, chiller, freezer etc? I'm trying to select a electrical compressor for a cooling load of about 0.8 ton.
    Apr 2006
    49
    1,920
    23
    Re: Evaporator temperature value
    general rule of thumb, is your evaporating pressure / saturated temperature is 10k below your required space temperature
    R's chillerman
    If the World did not Suck, We would all fall off !
    Jan 2013
    India
    27
    7
    I have a compressor datasheet. Its details are as follows..
    My cooling capacity is around 2500 Watts. My required temp is 25deg celsius. To use this compressor, I have to run it with rpm in between 2800 and 3700 rpm. The corresponding evap temp is 10deg celsius. Is this deduction correct or am I looking at a mismatched compressor?
    Aug 2007
    Sydney
    45
    1,093
    Hi princejoy
    That is a question different from the first. The compressor is med to hi temp and will do the job at 3700 but struggle towards 2800. So go for a bigger compressor. What rpm will you be using - fixed on voltage supply?
    Did you mean you cooling load as opposed to cooling capacity?
    Jan 2013
    India
    27
    7
    Quote Originally Posted by Tesla View Post
    My exact cooling load is around 2813Watts. Based on my understanding, I thought a rpm between 2800 and 3700 for a evaporator temperature of 12deg celsius(last column;mid- last and last before row) would do the job. Is my understanding correct?
    Jan 2013
    India
    27
    7
    I can also run the compressor at any desired speed with a constant voltage supply.(depends on the control circuit modification).