    Danfoss Compressor NL6F - no capacitor ok?



    I've recently ordered replacement electrics (PTC starting device) for a Danfoss NL6F compressor. The old PTC device - 103N0021 made use of a capacitor on the start winding, however the replacement - 103N0011 has no terminal for a capacitor, and it doesn't show a capacitor in the danfoss wiring diagram.

    Does this mean the compressor will run ok without a capacitor?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Danfoss Compressor NL6F - no capacitor ok?

    http://www2.renkulde.no/MKDokume.nsf/C322B3DE9C098D08C1256C2B0041CCB2/$FILE/NL6F_R134a_220V_50Hz.pdf

    data sheet shows a capacitor
    Last edited by install monkey; 06-02-2013 at 07:39 PM. Reason: hyperlink doesnt work, right click on web address and hey presto

  3. #3
    Join Date
    Mar 2009
    Location
    UK
    Posts
    29
    Rep Power
    0

    Re: Danfoss Compressor NL6F - no capacitor ok?

    If you look on the data sheet, there are two drawings. One labelled HST (which includes a capacitor) and the other labelled LST. I have the starting device shown in LST diagram which shows no wiring of a capacitor. I thought this was odd, but then again, I don't work with integral a very often.

  4. #4
    Join Date
    Mar 2009
    Location
    UK
    Posts
    29
    Rep Power
    0

    Re: Danfoss Compressor NL6F - no capacitor ok?

    Actually, just found the answer for myself in this documentation.

    http://utenti.multimania.it/cariafra...%20Danfoss.pdf

    Turns out you don't nessecarily need a capacitor in systems where the pressures equalises.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Danfoss Compressor NL6F - no capacitor ok?

    make sure the pot is off for 2-3mins to ensure system pressures equalize when off on stat

  6. #6
    Join Date
    Mar 2009
    Location
    UK
    Posts
    29
    Rep Power
    0

    Re: Danfoss Compressor NL6F - no capacitor ok?

    Quote Originally Posted by install monkey View Post
    make sure the pot is off for 2-3mins to ensure system pressures equalize when off on stat
    It's on a thermostat, not controller so I have no control over compressor start delay. It'll probably be over 5 minutes between cycles. Do you think I'm best ordered the HST electrics instead?