Results 1 to 4 of 4
Thread: filter alarm
-
05-02-2013, 10:14 PM #1
filter alarm
just installed a mitsi 3 pipe system all working ok but controllers keep coming up with clean filters
every few days which is starting to get a bit boring now got 4 fdtc 4 ways cassetts all with
RCE3 Wired Controllers is there any way i can adjust the time between service intervals to stop filter alarms
-
05-02-2013, 10:50 PM #2
Re: filter alarm
I know that the link I've given is for a different model but often the mode settings are the same across different units.
You can change the filter sign from the standard 100hours to either 2500hours or OFF, I prefer OFF on my Daikins 'cos it stops a lot of silly phone calls.
Go to page 86 of this manual...
http://www.mitsubishi-aircon.se/upl/files/53929.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
05-02-2013, 11:06 PM #3
Re: filter alarm
mitsi heavy ind- controller settings http://www.mediafire.com/view/?3nd09awxfsh332y
-
06-02-2013, 08:55 PM #4
Re: filter alarm
thanks guys those links were a big help