    Unhappy Help ! Carrier Gx30 chiller oil faults/ problems



    Ive recently started working for a new firm that has a large number of chillers on site, i come from an a/c and a fairly decent work / knoledge on chillers. I found a carrier chiller with fault codes that relate to oil pressures, i have reclaimed the refrigerant, change the oil solenoid, changed the filter cores on the drier, topped the oil up, made sure all service valves are back seated so they're open to the system, after all that i re charged it, started it up and it runs for 5 mins if im lucky. Goes out on fault '64' which so far as the manual says is a oil restriction, blockage or valve shut, ive checked so many times and dont seem to be getting very far help ! please



  2. #2
    Join Date
    Jan 2013
    Location
    uk
    Age
    34
    Posts
    8
    Rep Power
    0

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    forgot to mention i have tested the oil pump and seems fine !

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Have you checked/cleaned the internal oil filters and followed the 'top-up' procedures?

    Manual here...
    http://eto.carrier.com/litterature/i...30GX_HX_HR.pdf

    If you have a different model or want some others then check the Carrier data website....
    http://eto.carrier.com/lit.asp
    [scroll down thru' the models numbers and then click on 'search'
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Quote Originally Posted by mattblade View Post
    Ive recently started working for a new firm that has a large number of chillers on site, i come from an a/c and a fairly decent work / knoledge on chillers. I found a carrier chiller with fault codes that relate to oil pressures, i have reclaimed the refrigerant, change the oil solenoid, changed the filter cores on the drier, topped the oil up, made sure all service valves are back seated so they're open to the system, after all that i re charged it, started it up and it runs for 5 mins if im lucky. Goes out on fault '64' which so far as the manual says is a oil restriction, blockage or valve shut, ive checked so many times and dont seem to be getting very far help ! please
    Check your oil pressure transducer and economizer transducer. Alarm 64 which mention the max difference between the economizer pressure and oil pressure, also check the control circuit especially any loose connection on the port of connected to the respective board.

  5. #5
    Join Date
    Dec 2011
    Location
    Ireland
    Age
    43
    Posts
    51
    Rep Power
    13

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    If it has 2 circuits and 2 screw compressors there is an internal oil filter in the compressor. a little bit hard to get out need a large allen key head on a ratchet to turn the cover. cant remember what size but its a big allen head possibly about 40mm. once removed u can replace the filter quite easily.
    I had similar problems and replaced the internal filter and the external filter near the small oil pump. oil filter should be wrapped with a heater. i did this a little while after the oil pump was replaced and all was ok. does the pump come on at the start sequence to increase oil pressure before comp starts. will attempt to reach oil pressure 3 times before alarming out from memory.


    "9.5 - Oil pumps
    The 30GX/HXC screw chillers use one externally mounted
    pre-lubricating oil pump per circuit. This pump is operated as
    part ot the start-up sequence.
    ATTENTION: The operating temperature of the coil may
    reach 80°C. In certain temporary conditions (especially
    during start-up at low outside temperature or low condenser
    loop temperature) the oil pump can be reactivated.
    On 30GX units, the pumps are mounted to the base rails on the
    oil separator side of the unit. The pumps are mounted to a
    bracket on the condensers of 30HXC units. When a circuit is
    required to start, the controls will energize the oil pump first so
    that the compressor starts with correct lubrication. If the pump
    has built up sufficient oil pressure, the compressor will be
    allowed to start. Once the compressor has started, the oil pump
    will be turned off. If the pump was not able to build up enough
    oil pressure, the control will generate an alarm"

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Check your oil heaters and internal oil filters as already mentioned and its a 19mm Allen key needed

  7. #7
    Join Date
    Oct 2008
    Location
    FRANCE
    Age
    58
    Posts
    13
    Rep Power
    0

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    you say , you have check the oil pump (black model ) , when the pump is broken, the internal parts off the pump are going in cooper pipe, and stay just in connector brass inlet oil port compressor , ( currently the spring , teflon ball, and snap ring, you can check at this point, because this coonector is smaller diameter inside .
    Close the manual valve after the pump, evacuate oil and refrigerant by 1/4 schrader after the oil selenoid compressor, diconnect the nut on brass connector and look inside , maybe your problem is here !! Good job

  8. #8
    Join Date
    Jan 2013
    Location
    uk
    Age
    34
    Posts
    8
    Rep Power
    0

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    thanks for the replys, changed both the oil filters, and the 2nd circuit works a treat, now ive got a hp fault on circuit 1 that wont reset :/, theres nothing causing it to go out on hp, it doesnt even fire up

  9. #9
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Faulty HP switch ?????

  10. #10
    Join Date
    Jan 2009
    Location
    england
    Posts
    17
    Rep Power
    0

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    send me your email or google Carrier 30gx pro dialogue.... manual shows you how to read the pressures

  11. #11
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Hi mate
    you need an 19mm Allen key socket remove both internall oil filters within the the compressor also replace the external oil filters this will resolve your oil pressure problem also on 30gx chillers this is a common problem on your service visit always check the delta p across the oil filter should be no more than 150kpa diff also the check valve in the oil line is prone to fail recommend replacing with the Henry check valve

  12. #12
    nhuzain's Avatar
    nhuzain Guest

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    carrier 30gx chiller discharge gas temperature is high above 210 what is the resan

  13. #13
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Could be many reasons. See attached.

    http://www.achrnews.com/articles/wha...ge-temperature

  14. #14
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Hi
    usually on 3ogx if your discharge temp is high it could be either low charge ergo a leak
    or bad eco solonoied.
    possibly a faulty sensor .
    i would double check with your own thermometer make sure it is really running hot check pressures
    and act accordingly
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  15. #15
    Join Date
    Sep 2010
    Location
    Kazakhstan
    Age
    51
    Posts
    36
    Rep Power
    0

    Re: Help ! Carrier Gx30 chiller oil faults/ problems

    Hi! Does anybody has info about pro-dialog service menu and parameters in it? After entering 88 password.
    Chiller – carrier 30hw141. Pro-dialog g&h.
    Thanks…