    compressor failure Hall Screw 4221



    Good day!
    Ask for advice on the compressor
    After 3 years of operation of the compressor started to warm up. After dismantling babbit found flaking on the drive shaft and rubbing on one of the Capacity Control Slides.
    Because of what it could be? The compressor runs on ***** 134, cools glycol.
    By the way, who knows what they are covering the edge of the shaft babbitt?

    IMG_2990.jpgIMG_2991.jpgIMG_2984.jpgIMG_2985.jpgIMG_2986.jpg



  2. #2
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    3.jpg
    Capacity Control Slides.

  3. #3
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    1.jpg
    Capacity Control Slides

  4. #4
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: compressor failure Hall Screw 4221

    http://www.halltherm.com/

    I say get a new / rebuild compressor. The hassle & liability of trying to repair that kind of damage is too much. Be sure to check for liquid slugging & correct operating pressures / temperatures - that kind of damage in 3 years points to a problem with compressor operating conditions.

  5. #5
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    Working pressure of 134a ***** rarely rose above 9 bar.
    In this compressor had problems with the evaporator: rotten pipe and glycol got into the ***** part.

  6. #6
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    The fact that this is a semi-hermetic compressors and spare parts to it do not sell. At least, that's explained in the Ukrainian representative

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: compressor failure Hall Screw 4221

    In this compressor had problems with the evaporator: rotten pipe and glycol got into the ***** part.
    Lack of lubrication = abnormal wear.
    You can hardly blame the compressor if the refrigeration circuit got flushed with Glycol.

    I am not sure of your comment about spares but as far as I know J&E Halls spares network is excellent.
    I can't comment upon the price though!
    Which is all irrelevant as the comp is not designed to handle Glycol!
    Grizzly

  8. #8
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    Thank you, I understand your point.
    In your opinion, the Capacity Control Slides should be changed?
    Why Manufacturer afloat Babbitt on the drive shaft?

  9. #9
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    Quote Originally Posted by Grizzly View Post
    Which is all irrelevant as the comp is not designed to handle Glycol!
    Grizzly
    Yes, this is the problem: given a tube evaporator leak.

  10. #10
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: compressor failure Hall Screw 4221

    Hi i think the babbitt is there to protect the main shaft and body rubbing together and causing expensive damage, when the babbitt comes off the compressor it does,nt pump,eg when bearings wear ,or screw over heats it gets shaved off or peels instead of rubbing and grinding into the body. the gap between the body and screw is about 4 thou and the repair is easy for manufacture ,just spray or use other method to put babbitt on the screw.

  11. #11
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: compressor failure Hall Screw 4221

    Hi are you sure that it is Babbitt? I would personally assume that it is pick up from micro seizure as the lubrication film breaks down either from flushing or tolerance changes as the liquid entered compressor.

    You can check if it is Babbitt (White Metal) by scraping some and testing if magnetic.
    I love the smell of Ammonia in the morning!

  12. #12
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    Yes, it is 100 % babbit.

  13. #13
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    49
    Posts
    9
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    Who can tell you where you can buy the main rotor? Repairing the damaged rotor exempt. I would like to hear the opinion of the representative J&E Hall.
    Thank you!

  14. #14
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: compressor failure Hall Screw 4221

    Yes it is a white metal covering, hit with ball bearings to increase oil pickup. Do not rebuild this machine its not worth it. Just buy a new one from spares distributor. Oh and fix the evaporator and new oil charge etc....

    Just seen pics too, you'll need to replace bearings and slides too as bearings have dropped and caused the damage seen.
    Last edited by HallsEngineer; 24-04-2013 at 01:45 PM.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?

  15. #15
    Join Date
    Oct 2001
    Location
    Barranquilla , Colombia
    Age
    74
    Posts
    31
    Rep Power
    0

    Re: compressor failure Hall Screw 4221

    I know similar cases and treated "Plating" waste when synthetic oil reacts with water and pipe heat exchangers and other metal surfaces forming a paste.

    On my desk I have a rotor of J & E Hall to work weeks without oil . It is the best refrigeration compressor .

    Suggest clean all parts , replace bearings and stars in fiber. . . and ready


    Please , see www.cbarrantes.com/english.html

    Regards