    effects of a blocked condenser -evaporator



    hi there

    i have a quick couple of questions about the refrigeration circuit

    If a condenser does not work properly the refrigerant cannot cool properly so you would get low subcooling , would this mean that not all the refrigerant would not be subcooled liquid ,



    if it cannot that means (i think ) there is not going to be enough super heating causing the refrigerant to turn back to low pressurre super heated vapour to early which means it cannot remove enough heat from the refridgeratated space

    what would this look like on the gauges would i have a high low side pressure and a high high side pressure



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: effects of a blocked condenser -evaporator


  3. #3
    Join Date
    Jan 2013
    Location
    uk
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: effects of a blocked condenser -evaporator

    thank you thats a very good chart and will be very useful