Thread: Flooded Evaporator?
-
02-02-2013, 12:34 PM #1
Flooded Evaporator?
Hey friends I want to know in Flooded Evaporator Why the tube Carrying water are Half filled in Shell?Upper portion of shell is empty and lower shell carrying tubes?
-
02-02-2013, 03:09 PM #2
-
02-02-2013, 04:41 PM #3
Re: Flooded Evaporator?
Hi Mayan.
Are you viewing this "water" (I see where you are going Rob!) through a site glass with a centrif compressor
above the evaporator?
The question is relevant, given the little amount of information you give.
Grizzly
-
03-02-2013, 05:41 PM #4
Re: Flooded Evaporator?
I mean The Shell Congaing Refrigerant is Half fill of tubes which contain Water.I am attaching a Similar Image.
-
03-02-2013, 11:23 PM #5
Re: Flooded Evaporator?
See
http://nptel.iitm.ac.in/courses/Webc...cture%2023.pdf
Section 23.4.1 on page 6
There is a good explanation.
Basically it gives the refrigerant space to help liquid droplets settle.
Regards
Rob
... ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..
-
Re: Flooded Evaporator?
What he said
It's extra space to prevent liquid droplets to follow the gas stream into the compressor.
on coolers with a full set of tubes in the shell you will have an "expansion" tank on top like in this picture:
MMC_KVA.jpg-Cheers-
Tycho
-
04-02-2013, 07:37 PM #7
Re: Flooded Evaporator?
ThankS Rob...It helped...