    Dec 2012
    Dubai
    42
    Lightbulb Flooded Evaporator?
    Hey friends I want to know in Flooded Evaporator Why the tube Carrying water are Half filled in Shell?Upper portion of shell is empty and lower shell carrying tubes?
    May 2012
    54
    1,309
    30
    Re: Flooded Evaporator?
    Quote Originally Posted by MayankBhatia View Post
    Are you saying the shell and tube is only
    half full of water?
    Rob
    Somerset
    64
    4,581
    Hi Mayan.
    Are you viewing this "water" (I see where you are going Rob!) through a site glass with a centrif compressor
    above the evaporator?
    The question is relevant, given the little amount of information you give.
    Dec 2012
    Dubai
    42
    I mean The Shell Congaing Refrigerant is Half fill of tubes which contain Water.I am attaching a Similar Image.
    May 2012
    54
    1,309
    30
    See
    http://nptel.iitm.ac.in/courses/Webc...cture%2023.pdf
    Section 23.4.1 on page 6
    There is a good explanation.
    Basically it gives the refrigerant space to help liquid droplets settle.
    Rob
    Jan 2006
    Norway
    40
    799
    4
    22
    See
    Rob
    What he said
    It's extra space to prevent liquid droplets to follow the gas stream into the compressor.
    on coolers with a full set of tubes in the shell you will have an "expansion" tank on top like in this picture:
    -Cheers-
    Tycho
    Dec 2012
    Dubai
    42
    ThankS Rob...It helped...