    Understanding Daikin service checker



    Chaps
    we are having an EO error on a K-plus system. We know the module but pinpointing what is casing it is proving tricky

    I am willing to admit i really haven't got the foggiest idea on how the checker truly works so if anyone can have a look at the data and tell me if they can 'see' anything I'd be most gratefulchecker 3.jpgchecker 2.jpgchecker 1.jpg



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Understanding Daikin service checker

    Not so sure the checker will help you finding the fault... It will only present a lot of data to you for you to judge what is happening in the system.

    E0:
    -High pressure
    -Fan motor or compressor overload
    -broken wire harness
    -Loose connection
    -Outdoor PCB

    So;
    How often does it trip?
    In picture 3, where the suction pressure is just 1.3 bar, how long has the system been running for? Stable?
    Does the discharge temp stay that low or is it creeping up?
    Is the system running in heating, cooling or mixed?
    Has the charge been verified?
    Has the compressor and fans been megged?

    Happy hunting.



    .

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Understanding Daikin service checker

    From the pictures, you can see that the error is generated on Outdoor Unit 4. On this unit, compressor 1 is shown as ON but the sensor readings do not show that it is doing any work.

    Look at the left hand Numbers - O-1, O-2, etc. Outdoor unit 1, Outdoor unit 2 ..... As you have connected the checker via the pcb connection (top header) you won't be able to see the whole system. You need to connect via F1, F2 for this. Although for an EO fault this won't matter.

    Bear in mind that the checker software always generates an extra outdoor unit - the software (pcb) so it's not always easy to determine which is Unit 1, Unit 2 etc.

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Understanding Daikin service checker

    Thanks Frank. That shows you know way more than me..

    Update: Called in today and found 3rd module no/1 comp DTE.

    Isolated it and it is now back an running but the Maintenance manager is in for another 2.5k bill on Monday :-)

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Understanding Daikin service checker

    Always up for a virtual pint Richard....

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Understanding Daikin service checker

    Interesting stuff.
    In my Grease Monkey days when we used the scanner for engine management systems I found the data list very helpful to confirm fault codes or to pinpoint running faults when no fault code generated.
    Sadly in my AC reincarnation I've not had the opportunity to get my hands on this stuff. No matter, my day will come...

    If E0 is HP or fan error then how does a DTE compressor generate this code?

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Understanding Daikin service checker

    The pcb gives out and receives back a voltage to the compressor/fan motor(s). If this voltage is interrupted an EO error occurs. Normally on the grey wires/plug attached to the pcb.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Understanding Daikin service checker


  9. #9
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Understanding Daikin service checker

    Quote Originally Posted by frank View Post
    .

    Bear in mind that the checker software always generates an extra outdoor unit - the software (pcb) so it's not always easy to determine which is Unit 1, Unit 2 etc.

    For future reference:
    R22 K series plus systems consist of 2 or 3 outdoors & 1 function unit (valve box) this is why you see 4 outdoors in total. (Only VRV II/III/IV will show an additional target outdoor, allowing you to see the system target conditions at that time)

    E0 - R22 K plus
    1. Each outdoor unit has an orange fault light located at the bottom of the electrics box, this will indicate which unit has caused the fault and should be checked before attempting to reset the fault.
    2. Confirm the associated saftey circuit switches are closed circuit on this unit (with light illuminated)
    3. Try to reset fault from local remote controllers, if you can reset = Fan motor over heat klixon
    4. If the fault can only be reset by switching main power off/on at outdoor = compressor overload (latching circuit requiring power reset to clear)
    Last edited by VRVIII; 04-02-2013 at 07:52 PM.

  10. #10
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18
    He VRV III how are you.?
    Yes it's true the old lamp indicator, on each outdoor... The best way to match a faulf on old series.
    Now it's different even with service checker you've to read and understand the whole docs as data book, service manual, installation manual, operation manual, option manual.
    But sometimes it's even difficult to get documents...
    If you're not to busy just take a look at my previous thread about VRV IV, your posts are usually hepful.
    Kind regards
    Cool#9

    Sent from my Nexus 7 using Forum Runner

  11. #11
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Understanding Daikin service checker

    So am I correct in thinking a service checker will pick up the error but won't pin point it?

  12. #12
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Understanding Daikin service checker

    See the service checker as all the testers and gauges from your toolkit built in to one and multiplied.

    It tells you everything you need to know about the system but what you do with that knowledge is up to you.
    Also, what it tell you and how it is presented will vary depending on which generation of VRV you are looking at



    .

  13. #13
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Understanding Daikin service checker

    I find the service checker very helpful when looking at the data afterwards (normally in Starbucks), as it does not display the system conditions in real time, that could be the slow processing speed of my mind though!

    Also when first connecting a quick glance at thermistor and transducer readings will indicate their condition, an invaluable device as you can also control the indoor units, but I still find that if I am having difficulty finding a fault then it's always the traditional approach that I have the most success with.

    It would be interesting to hear how everyone else uses the checker, I am sure that there are many features that I am not familiar with.

    Cheers