    Daikin e4



    Guys

    I have a daikin 407c outdoor going out on a e4 fault after about 20 mins of restarting in heating mode .I was on the site briefly and only got to check the suction pressure at the compressor which hovered around 2 bar for 10-15 mins but then starting dropping and eventually goes into a vacuum before faulting out. So i assume the lp switch is ok . I'm back there tomorrow so just wondering if anyone had any ideas. The ambient temp was around 5 , I know 407c has problems at lower temps , I don't like daikin!!!!

    FHTCP125B7V1. Indoor x2
    RYP250B7W1 outdoor

    Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin e4

    E4
    Activation of low pressure sensor........

    Defect of low pressure sensor
    Defect of outdoor PCB or
    SOG

  3. #3
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin e4

    Thanks frank, keep it simple , love it . Would a faulty board cause the lp fault though , it obviously must be sog

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin e4

    Daikin say it could...but I would be inclined to recover the charge and take that out of the equation before anything else...

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin e4

    same as the Panasonic urban cu250h1spp- outdoor lev not opening- stick it in test cooling and check ur running pressures

  6. #6
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin e4

    That's what I was wondering monkey was something restricting gas flow??? I agree though frank, have the right gas charge gives me a strange warm feeling .

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin e4

    Panasonic part number cpd 101008j part b10- not listed on a exploded view parts list- b10 is the reference! good luck

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin e4

    Common problem of some models, do as Frank says, check the gas.

    Units will run for some time with gas shortage and then start dropping the pressures as you have seen. Next fault will be high discharge temperature.....
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jan 2009
    Location
    england
    Posts
    17
    Rep Power
    0

    Re: Daikin e4

    check indoor coil temp (code41)

  10. #10
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin e4

    Thanks lads,

    Got it sorted , in a way. The system with the e4 fault I couldn't get any good out of it, I recovered the gas, weighed in the correct new charge but the unit still went out on fault after 20 mins. So basically what I did was , there are 2 other identical systems on this site which have been awaiting repairs fans, pcbs, but there hasn't been any go ahead on it for the past few years. So I used good parts from the e4 unit to get one of these units running, happy days.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin e4

    did u use a long gauge line?? haha
    Quote Originally Posted by ronaldo9 View Post
    Guys

    I have a daikin 407c outdoor going out on a e4 fault after about 20 mins of restarting in heating mode .I was on the site briefly and only got to check the suction pressure at the compressor which hovered around 2 bar for 10-15 mins but then starting dropping and eventually goes into a vacuum before faulting out. So i assume the lp switch is ok . I'm back there tomorrow so just wondering if anyone had any ideas. The ambient temp was around 5 , I know 407c has problems at lower temps , I don't like daikin!!!!

    FHTCP125B7V1. Indoor x2
    RYP250B7W1 outdoor

    Thanks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •