    Thumbs up Sight glass location



    Recently there was a discussion(arguement) among our techs as to the correct location of the liquid line sight glass.Some say it should be before,some say after, others say it does not matter if its before or after the drier. I would like know what other techs think on this subject.



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Installing sight glass downstream of the liquid line filter-drier:

    Pro: one can see the condition of the refrigerant as it enters the expansion device. If the expansion device is starving, checking for the presence of flash gas ahead of it is normally one of the first things to consider.

    Con: if the sight glass shows flash gas, one does not know if it is the result of a low refrigerant charge, or a restricted filter-drier.

    Installing tight glass upstream of the liquid line filter-drier:

    Pro: if flash gas is present in the sight glass, it will not be the result of a restricted filter-drier. One can have a high confidence level that the system has a low refrigerant charge.

    Con: one cannot see the condition of the refrigerant as it enters the expansion device. If the evaporator is starving, and the sight glass is clear, one can only speculate the filter-drier is restricted. One can sometimes detect a restricted filter-drier by measuring a temperature drop across it. But this technique is often not reliable. Significant pressure drop can occur across a liquid line filter-drier at low delta T.

    Of course, the Prof has a solution the above debate: install two sight glasses.... one upstream and one downstream of the filter-drier....

    Assuming one didn't want to go thru the trouble and expense of installing two sight glasses, the Prof opts for placing it downstream of the filter-drier. If a system is not properly cooling, it is important for the technician to determine if the expansion device is operating properly. And that can be more easily accomplished by knowing the condition of the refrigerant entering it.
    Last edited by Prof Sporlan; 22-09-2001 at 02:59 PM.
    Prof Sporlan

  3. #3
    Join Date
    May 2001
    Location
    Trinidad,West Indies
    Posts
    16
    Rep Power
    0

    Thumbs up sight glass location

    Hey Prof's, thanks for the response. I am going to share this info with the rest of the techs. Hope it doesn't start another "debate"

  4. #4
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    All the replys are good ones but I would be aware that they only relate to large airhandlers. On mini splits expect to see bubbles in the sight glass otherwise the system is probably overcharged.

    Me I would probably purt the site glass before the filter drier but I think we can all agree before or after they are both valid.

  5. #5
    Join Date
    Apr 2002
    Location
    Nova Scotia, Canada
    Age
    55
    Posts
    22
    Rep Power
    0
    I always install the sight glass downstream of the
    filter drier. I like to see the condition of the liquid going to the TXV. If there is flash gas present and a plugged drier is the cause, you will usually be able to detect a noticable temperature
    drop from the inlet to the outlet.

  6. #6
    Join Date
    Mar 2002
    Location
    Tehran
    Age
    55
    Posts
    38
    Rep Power
    0
    Your discussion was very usefull .
    But I want to know if it is necessary installing a flat sight glass at the middle of receivers body .and what level of liquid is satisfied in it (at normal operation)?
    thanks.
    s.pirs
    S.P

  7. #7
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    I say a sightglass has one real use: as a moisture indicator. You should know the moisture content after the drier. Plus what the prof said able the valve getting a solid column of liquid.

  8. #8
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi,Pirestanti, I think you are asking about the liquid level in a liquid receiver. The glass shows a level from 10% to 80% aproximately. Define normal operation, if you are feeding one source (valve or vessel) or muliple. On a receiver feeding one device the level will drop at peak loading(due to a shortage or an inadequate receiver size) or when the evaporator is at it's lowest temperature. A range of levels is permissible for normal operation.
    Regards. Andy.
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Replies: 19
    Last Post: 18-07-2006, 08:16 PM
  2. Sight glass , Flashing ?
    By kfjoe in forum Fundamentals
    Replies: 15
    Last Post: 14-02-2004, 04:41 AM
  3. Sight Glass Located
    By Abe in forum Trouble Shooting
    Replies: 3
    Last Post: 22-01-2002, 01:22 AM
  4. Sight Glass,
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 03-08-2001, 08:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •