Hello friends im working on daikin vrv refrigerant r407c and i would be grateful if any body has a service manual on it.Thankyou
-
29-01-2013, 08:44 PM #2
Re: Daikin rseyp10kjy1
-
29-01-2013, 09:11 PM #3
Re: Daikin rseyp10kjy1
thankyou install monkey
-
29-01-2013, 09:34 PM #4
Re: Daikin rseyp10kjy1
did you get both manuals- I posted the links seperatly but they seem to have merged
-
29-01-2013, 09:44 PM #5
Re: Daikin rseyp10kjy1
Hi i only got 1, i check it again
-
29-01-2013, 09:51 PM #6
Re: Daikin rseyp10kjy1
ive got it now friend
-
29-01-2013, 10:36 PM #7
Re: Daikin rseyp10kjy1
I had a k series faulting once- no alarm code, started up for 3 seconds,compressor stopped- spent 5 days checking things- had 15 compressors on it- turned out to be a low press transducer thinking it had no gas in it- replaced the transducer,all ok- checked all sensor resistances, daikin tech no help as they said if theres no alarm code then theres no demand- check 3 ph supply!!