    liquid line distributor



    I have some brazed plate HE and they came without distributors. The ports are too big and I want to reduce flash gas. Has anyone made them and if so, do you have a diagram?

    Thanks



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: liquid line distributor

    Quote Originally Posted by MikeHolm View Post
    I have some brazed plate HE and they came without distributors. The ports are too big and I want to reduce flash gas. Has anyone made them and if so, do you have a diagram?

    Thanks

    I'm confused Mike? (I know, I know it doesn't take much )
    I thought Brazed plate heat exchangers only had one entry and one exit
    (refrigeration side) so how would a distributor after the expansion valve
    fit?

    Or am I being realy dense now

    Rgards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: liquid line distributor

    In my case, the port size is 1- 3/8" and it goes right to the back of the HX( of course). The liquid line in this case is a 3/8" so there is a large area for the refrigerant to flash so i want to reduce that volume if possible. The distributor needs to be an elongated liquid line that goes right to the back of the HX like a manifold to try and give equal flow and take up some of the volume at the same time.

    I've done this many times but not in a BPHE so i was wondering if there was a particular way they were built to reduce the open volume.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: liquid line distributor

    Any chance of getting a distributor from the HE makers?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: liquid line distributor

    Stupidly, I already brazed in the reducer before I thought about the distributor. I'm sure i can make it but a picture would be nice.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: liquid line distributor

    Mike. How about taking a picture or 2 of your Heat exchanger so we can see what you're trying to achieve.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: liquid line distributor

    Hi Mike
    FYI as i am no expert on your question but it intrigued me!
    http://www.google.com/patents/US5806586

    The drawings are useful for the description of operation, although I would never advocate commercially producing unlicensed patents, we leave that for certain global producing companies.

    hope it helps
    I love the smell of Ammonia in the morning!

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: liquid line distributor

    .

    So I was being dense

    I see your point and Hookster's solution seems a good one but you have
    brazed in a reducer already. What size have you reduced it down to?

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  9. #9
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: liquid line distributor

    Quote Originally Posted by Rob White View Post
    .

    So I was being dense

    I see your point and Hookster's solution seems a good one but you have
    brazed in a reducer already. What size have you reduced it down to?

    Regards

    Rob

    .
    1-3/8" port down to 3/8". It leaves a BIG area inside. Seeing the patent drawing, cut off the reducer and I can make a brass one that will fit inside the bigger part of the reducer. Not very pretty but doable. My mentor suggested I turn the holes down or sideways, rather than up, to move the refrigerant that sits at the bottom.

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: liquid line distributor

    Hi Mike.
    the BPHX's I have used come with an injector type tube with a linear laser cut slot that acts as the distributor, they have an alignment marking so as to feed circuits correctly. Slide it in, align and weld in place.

  11. #11
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: liquid line distributor

    Quote Originally Posted by Magoo View Post
    Hi Mike.
    the BPHX's I have used come with an injector type tube with a linear laser cut slot that acts as the distributor, they have an alignment marking so as to feed circuits correctly. Slide it in, align and weld in place.
    Do you have a link to them?

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: liquid line distributor

    WTT out of Germany.

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: liquid line distributor

    Install a liquid line/suction line h/e, fit the TEV bulb after the h/e, this will reduce the flash gas a basically flood the bottom port.

  14. #14
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: liquid line distributor

    Quote Originally Posted by mad fridgie View Post
    Install a liquid line/suction line h/e, fit the TEV bulb after the h/e, this will reduce the flash gas a basically flood the bottom port.
    The liquid from the condenser goes through a short "tube in tube" HE on the comp suction line, then to the pancake coil in the accumulator, then through a subcooling valve, then to the Evap which is on the same level as the valve. The bulb is on the line entering the "tube in tube HX". There is nothing between the comp and the condenser inlet. I should have at least 10-15C subcooling prior to the evap (BL50 30plate HE) and it is designed to be partially flooded.

    I was told that Alfa laval had trouble years ago in highly subcooled evaps with out distributors, freezing out one side of the HX and splitting it. I just want to get equal flow and I am not sure that there will be any real flash in this design but I could be surprised.

    Mad, where you have placed the TEV?
    Last edited by MikeHolm; 31-01-2013 at 12:21 PM.

  15. #15
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: liquid line distributor

    Quote Originally Posted by Magoo View Post
    WTT out of Germany.
    Just finding general links. Time to phone manufacturers.