    Unhappy Help ry100fj7v1



    Wondering if anyone can help me as I'm having a nightmare with this system! Daikin RY100FJ7V1 ducted on R22! Found system to be short of gas, found leak and re commissioned. Then would only get 30 degrees on the coil (41 settings) re claimed system and changed expansion valve and head and re charged! The system is still doing the exact same thing. Boss is going wild and I'm back up on the snowy roof trying to fix it again Monday! Any ideas would be handy I'm thinking Outdoor PCB. System has no faults logged. Cheers



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Help ry100fj7v1

    Short of charge? (have you measured the pipework and recalculated the total charge)
    Lack of airflow across/around the outdoor unit? (Is the coil clean, the fan running flat out and nothing behind or in-front of the unit)
    Is the compressor pumping properly? (This is an old lady at the end of her game, a pumpdown test will give you an indication of her efficiency)

    After the above has been checked (Oh, I do assume you took a deep vacuum on her and used OFN whilst you were brazing) you need to start looking at pressure/temperature relations.
    It is unlikely that it will be an electrical/control issue, they tend to either stop the unit completely or not be present...



    .

  3. #3
    Join Date
    May 2010
    Location
    West Sussex
    Age
    34
    Posts
    5
    Rep Power
    0

    Re: Help ry100fj7v1

    Quote Originally Posted by The Viking View Post
    Short of charge? (have you measured the pipework and recalculated the total charge)
    Lack of airflow across/around the outdoor unit? (Is the coil clean, the fan running flat out and nothing behind or in-front of the unit)
    Is the compressor pumping properly? (This is an old lady at the end of her game, a pumpdown test will give you an indication of her efficiency)

    After the above has been checked (Oh, I do assume you took a deep vacuum on her and used OFN whilst you were brazing) you need to start looking at pressure/temperature relations.
    It is unlikely that it will be an electrical/control issue, they tend to either stop the unit completely or not be present...



    .
    Thanks for the reply! I have done everything you said apart from the compressor pump down test and was actually thinking about this when I was driving home! If the unit was a German Sheppard you would take it to the bets to be put down but the client wants to try get it running!

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Help ry100fj7v1

    Quote Originally Posted by Craig22 View Post
    Wondering if anyone can help me as I'm having a nightmare with this system! Daikin RY100FJ7V1 ducted on R22! Found system to be short of gas, found leak and re commissioned. Then would only get 30 degrees on the coil (41 settings) re claimed system and changed expansion valve and head and re charged! The system is still doing the exact same thing. Boss is going wild and I'm back up on the snowy roof trying to fix it again Monday! Any ideas would be handy I'm thinking Outdoor PCB. System has no faults logged. Cheers
    Why did you change the valve and why do you now think it is the pcb?

  5. #5
    Join Date
    May 2010
    Location
    West Sussex
    Age
    34
    Posts
    5
    Rep Power
    0

    Re: Help ry100fj7v1

    Quote Originally Posted by r.bartlett View Post
    Why did you change the valve and why do you now think it is the pcb?
    Was only getting 10 degrees difference in heating and cooling on the coil! Changed expansion valve and head! Maybe thinking the PCB isn't opening the expansion valve enough

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Help ry100fj7v1

    You need to post some temperature and pressure readings so that a proper diagnosis can be made instead of guessing whats wrong

  7. #7
    Join Date
    May 2010
    Location
    West Sussex
    Age
    34
    Posts
    5
    Rep Power
    0

    Re: Help ry100fj7v1

    Quote Originally Posted by frank View Post
    You need to post some temperature and pressure readings so that a proper diagnosis can be made instead of guessing whats wrong
    3 bar suction, haven't taken discharge 20 degrees air on 30 air off in heating 7 in cooling. Seems like condensor is running well outside just not getting the duty inside! Just trying to see if anyone's had this before

  8. #8
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Help ry100fj7v1

    Quote Originally Posted by Craig22 View Post
    3 bar suction, haven't taken discharge 20 degrees air on 30 air off in heating 7 in cooling. Seems like condensor is running well outside just not getting the duty inside! Just trying to see if anyone's had this before
    Have you got a faulty changeover or have you just posted your condensing figures wrong?
    I love the smell of Ammonia in the morning!

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Help ry100fj7v1

    Quote Originally Posted by Craig22 View Post
    3 bar suction, haven't taken discharge 20 degrees air on 30 air off in heating 7 in cooling. Seems like condensor is running well outside just not getting the duty inside! Just trying to see if anyone's had this before
    So you have 30 degrees C coil temp but also 30 degrees C air off the indoor unit?

    As Frank says more pressure/temps are required to help with the diagnosis.

    Suggest

    Discharge pressure or liquid pressure (SCT)

    Discharge temperature after the compressor

    Liquid temperature

    Suction temperature

    Suction pressure (SST)

    Air on/off indoor

    Air on/off outdoor

    You need to see if the discharge temperature from the compressor is much higher than your indoor coil temp, if it is then start with looking at the 4 way reversing valve.

    If its not then start looking at low superheat flooding the compressor which will affect the discharge temperatures.

    Again without knowing the temps & pressures its just guessing
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Help ry100fj7v1

    And...

    Accurate figures is needed.
    Your 3 Bar, sure it wasn't 2.95 or 3.07???

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Help ry100fj7v1

    http://www.mediafire.com/view/?epjaejoexnr50dp http://www.mediafire.com/view/?6r7q2k2nebsrukf http://www.mediafire.com/view/?g0ode3h8rvhhzx1 bit of literature into the operation of units-any red led 1,2 flashing or on on the outdoor??- measure piperun,check strainers aren't clogging