    Thermostatic expansion valve



    Hiya
    I have a flakt woods condensing unit that's on r407c and is 28kw. It has 2 stages which are to be connected to a air handling unit. I need to size for 2 externally equalised TEVs for the application. I know the evaporating temp is obviously 0degrees for the system, do I size for 2 14kw valves? And also iv noticed the different pressure drops across the valve options. Iv always got the standard 8 bar differential for other applications will this still be fine?
    personally I think I need 2 TEZ2 valves with number 5 orifaces? Just would like a second opinion.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Thermostatic expansion valve

    TEZ2 and n.5 gives 10.5 kw at 5'C according to Climate book. Think also if there is a distributor you may need to oversize to account for the extra pressure drop through the distributor and thinner pipes (could be wrong about this though...)

    I'd get the wholesalers tech dept to size them if it was me.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Jan 2008
    Location
    derbyshire
    Posts
    15
    Rep Power
    0

    Re: Thermostatic expansion valve

    i think its dependant on pressure drop the tez2 no 5 with 8bar pressure drop is 14.7kw. slighly confused