    hi new to this i have a couple of questions about presure temp



    hi there ,

    I am studying at the moment and have loads of questions the first one is about pressure temp

    on my chart for pressure temp it tells me that at 0oc the pressurre of r134a is 2.98 bar
    which is straight forward enough , but if my gagues tell me that the suction pressurre is 2.98 bar and my temp is zero in my evaporator were it is changing phase what will my air off be , it wont be 0oc

    is there a rule of thumb to tell you what your air off will be

    for example i want my freezer down to minus 10oc what pressurre would i want my r134a at to get me that temp



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: hi new to this i have a couple of questions about presure temp

    Quote Originally Posted by superduke View Post
    hi there ,

    I am studying at the moment and have loads of questions the first one is about pressure temp

    on my chart for pressure temp it tells me that at 0oc the pressurre of r134a is 2.98 bar
    which is straight forward enough , but if my gagues tell me that the suction pressurre is 2.98 bar and my temp is zero in my evaporator were it is changing phase what will my air off be , it wont be 0oc

    is there a rule of thumb to tell you what your air off will be

    for example i want my freezer down to minus 10oc what pressurre would i want my r134a at to get me that temp
    The evaporator is always the coldest and we normally work to a Rule of Thumb of 10degs difference.
    The evaporator will be about 10 degs colder than the air off the evaporator.
    If you want a case temp of -10 degC then you will be evaporating at approximately at -20 degC.

    But in your calculation you have mixed up gauge pressure and absolute pressures.

    We measure scientifically in pascal's (named after the guy who invented pressure )
    and there are two pressures there is the absolute pressure and then there is gauge pressure.

    Gauge pressure would show zero if you open your gauges up to the air you are stood in (under normal atmospheric conditions), but absolute would read 1 bar (or 100,000 and a bit pascal) so if you are looking
    on a compariter don't confuse the two pressure.

    Gage pressure is always the lower of the two and that is the one you use to measure the working system.
    Your 0 degC at 2.9 should be 0 degC at 1.9 (2 bar to you and me) when reading on a working system
    using gauges.

    Your "for example i want my freezer down to minus 10oc what pressurre would i want my r134a at to get me that temp"

    Case temp -10 degC = evaporating at about -20 degC = pressure of 0.3 to 0.4 barg.


    Regards

    Rob

    .
    Last edited by Rob White; 21-01-2013 at 04:17 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Jan 2013
    Location
    uk
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: hi new to this i have a couple of questions about presure temp

    aha that is superb , thank you very much .

  4. #4
    Join Date
    Jan 2013
    Location
    uk
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: hi new to this i have a couple of questions about presure temp

    and bar gauge as well i had not factored that in .

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: hi new to this i have a couple of questions about presure temp

    .

    Nice one.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..