    Reciever or not
    Should a reciever be used on a capiliary exp device system, I am replacing a small condenser set it comes with one fitted I suppose I could cut it off but can it be left on
    Oct 2007
    manchester
    44
    5,707
    Re: Reciever or not
    no, when selecting condensing units,you select duty and expansion device either capillary or txv
    44
    3,799
    38
    Re: Reciever or not
    Should not use reciever in cap tube system, it will fill the evaporator in the off cycle and then flood the compressor on re starting.
    Jun 2008
    NZ
    102
    11
    Re: Reciever or not
    Agree - but I have seen a freezer fitted with a solenoid as a liquid stop valve, wired in paralell with the comp to prevent exactly that problem.
    It was an Angelo Po if I'm not mistaken.
    Apr 2006
    35
    1,646
    Re: Reciever or not
    you gain nothing from it and it increases the refrigeration charge at no gain as well. I would personally remove it. The filter dryer serves as your mini receiver to ensure a liquid seal at the cap tube.