Results 1 to 8 of 8
Thread: pco carel alarm
    Jan 2010
    india
    38
    5
    pco carel alarm
    Hai !!
    Dear all
    I Have central frigo bitzer 75hp water cold condensing unit
    With carel rack controller in this controller shows alarm
    ALARM.. over load,K1ixon
    compressor 1
    But unit manual running is ok ......
    please suggest to resolve problems
    unit make ; central frigo 75 HP
    code ; 00240094501
    compressor make ; bitzer
    type ; screw
    model no ;HSN7471-75-40P
    controller ; carel rack controller
    code ; FLSTDMFC0A
    11,025
    Re: pco carel alarm
    Have you checked the Klixon?
    Jan 2010
    india
    38
    5
    Re: pco carel alarm
    hello Brian
    Yes i am checked compressor Relay this continuity is OK
    kirwan motor protectors also this continuity is ok
    I hope Klixon mines this motor protector & Relay
    any more please guide me
    Jan 2010
    india
    38
    5
    Re: pco carel alarm
    Hello Brian
    please reply to me because unit not working in auto mode
    it working mechanical mode only
    PCO alarm also not reset
    how solve this problem please .........?
    Jan 2010
    india
    38
    5
    Exclamation carel pco
    Dear all
    any carel pco service center in Hyderabad, Andhra pradesh,INDIA.
    Plase give contact details.
    Thanking you
    HUSSAIN
    Feb 2013
    10
    Re: carel pco
    hi
    if i know that are you looking for i can help you with technical issues
    or
    there is a carel india office , ask them :
    Carel ACR Systems India Private Limited (CAREL India)
    402 & 403 Vikas Commercial
    Next to Tridev Apartments
    Bhakti Marg, Mulund (West)
    Mumbai 400 080
    tel. +91 22 4119 2929
    fax +91 22 4119 2930
    info@carel.in
    Feb 2013
    10
    Re: pco carel alarm
    hi
    check the wiring first, you need to make sure the alarm coming from overload.
    basically controller presume ID1 (for example) as Comp 1 overload digital input, it means if by mistake you connect fan overload to ID1 in case of Fan alarm you are getting comp alarm.
    another thing can be the input latched in to closed position due to high current.
    Behzad
    Feb 2013
    india
    38
    1
    Re: carel pco
    Brian - Torquay, Devon, UK
    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.