Thread: pco carel alarm

  1. #1
    Join Date
    Jan 2010
    Location
    india
    Age
    38
    Posts
    5
    Rep Power
    0

    pco carel alarm



    Hai !!
    Dear all

    I Have central frigo bitzer 75hp water cold condensing unit
    With carel rack controller in this controller shows alarm

    ALARM.. over load,K1ixon
    compressor 1


    But unit manual running is ok ......
    please suggest to resolve problems


    unit make ; central frigo 75 HP
    code ; 00240094501

    compressor make ; bitzer
    type ; screw
    model no ;HSN7471-75-40P

    controller ; carel rack controller
    code ; FLSTDMFC0A
    Last edited by Brian_UK; 18-01-2013 at 07:56 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: pco carel alarm

    Have you checked the Klixon?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2010
    Location
    india
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: pco carel alarm

    hello Brian

    Yes i am checked compressor Relay this continuity is OK
    kirwan motor protectors also this continuity is ok

    I hope Klixon mines this motor protector & Relay
    any more please guide me

  4. #4
    Join Date
    Jan 2010
    Location
    india
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: pco carel alarm

    Hello Brian

    please reply to me because unit not working in auto mode
    it working mechanical mode only

    PCO alarm also not reset

    how solve this problem please .........?

  5. #5
    Join Date
    Jan 2010
    Location
    india
    Age
    38
    Posts
    5
    Rep Power
    0

    Exclamation carel pco

    Dear all

    any carel pco service center in Hyderabad, Andhra pradesh,INDIA.

    Plase give contact details.



    Thanking you

    HUSSAIN

  6. #6
    Join Date
    Feb 2013
    Location
    UK
    Posts
    10
    Rep Power
    0

    Re: carel pco

    hi

    if i know that are you looking for i can help you with technical issues
    or
    there is a carel india office , ask them :
    Carel ACR Systems India Private Limited (CAREL India)
    402 & 403 Vikas Commercial
    Next to Tridev Apartments
    Bhakti Marg, Mulund (West)
    Mumbai 400 080
    tel. +91 22 4119 2929
    fax +91 22 4119 2930
    info@carel.in

  7. #7
    Join Date
    Feb 2013
    Location
    UK
    Posts
    10
    Rep Power
    0

    Re: pco carel alarm

    hi
    check the wiring first, you need to make sure the alarm coming from overload.
    basically controller presume ID1 (for example) as Comp 1 overload digital input, it means if by mistake you connect fan overload to ID1 in case of Fan alarm you are getting comp alarm.

    another thing can be the input latched in to closed position due to high current.

    Behzad

  8. #8
    Join Date
    Feb 2013
    Location
    india
    Age
    37
    Posts
    2
    Rep Power
    0

    Re: carel pco

    Brian - Torquay, Devon, UK
    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •