    Freeze Up Auto Or Manual In Chiller?



    Hi

    can we use KP 59 thermostat DANFOSS MADE as freeze up thermostat mind u it is auto reset type in 70 HP water cooled water chiller
    i dont agree and maintain that manual should be selected as it is last safety for compressor and autoreset type is not suited.
    My question is can we use auto reset why and why not in both cases.

    URGENT REPLY NEEDED

    REGARDS

    ENGR. ALI ABBASI


    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  2. #2
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: Freeze Up Auto Or Manual In Chiller?

    auto reset is not recomended for me , cause we must find the reason for freezing chiller, then we reset the thermostat to other cycle of operation
    good day
    afeef

  3. #3
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: Freeze Up Auto Or Manual In Chiller?

    wat about people who are already using auto reset type thermostats
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  4. #4
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: Freeze Up Auto Or Manual In Chiller?

    dear abbasi
    you can check out the reason of freezing , like
    1-do you have ethylene-glycol mixed with chilled water?
    2-what is the evaporator tem. ? and the super heat degree
    3-is the evaporator clean from scale and salt deposits
    4-is the TEV working good?
    5-is the air-handling units&fan coils clean?
    6-may be the freez thermostat is faulty!
    good luck

  5. #5
    rbartlett's Avatar
    rbartlett Guest

    Re: Freeze Up Auto Or Manual In Chiller?

    I have seen some manufacturers using auto reset freeze stats..

    they usually have a delay timer in the control circuit which prevents short cycling.

    however make sure you set it to trip out slightly higher than usual and a wide diff.

    cheers

    richard

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Freeze Up Auto Or Manual In Chiller?

    I would only recommend the manual reset type.

    With the automatic reset switches, the chiller can have repeated freeze and thaw cycles as the switch automatically resets. Even if the manufacturer provides an auto reset switch, I would change it to a manual reset.

    You may sell a new evaporator after it freezes up and make some money, but this does not help the owner.

    The manual switch trips out and shuts the chiller off until someone can find the fault. This is the best way in my opinion.

  7. #7
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: Freeze Up Auto Or Manual In Chiller?

    hmmm
    so the case is not to use auto reset freeze up thermostat it is needless to set auto freeze up on temp higher than desired coz differential will be low
    Thanx for your suggestions
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  8. #8
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: Freeze Up Auto Or Manual In Chiller?

    I think manual resets on controls is the better way it forces some one to go to the unit and assumes that he or she will check unit and not just reset.

  9. #9
    ajmalparvez's Avatar
    ajmalparvez Guest

    Re: Freeze Up Auto Or Manual In Chiller?

    Hi Im ajmal Irecntly join refrigeration-engineer.com
    I have problem fine filter alarm with maycom screw comprassor can I bypas FF

    Thanks

    ajmal

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Freeze Up Auto Or Manual In Chiller?

    I have problem fine filter alarm with Mycom screw comprassor can I bypas FF?
    NO, NO, NO...

    Change the filter elements. And check the filter differential to make sure the differential is actually what the alarm is for.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. chiller freeze up
    By cletus in forum Technical Speculations
    Replies: 41
    Last Post: 21-03-2006, 10:32 PM
  4. chiller manual
    By zimbo in forum Training
    Replies: 2
    Last Post: 28-01-2006, 05:38 AM
  5. HP Switches (Manual or Auto)
    By Latte in forum Technical Discussions
    Replies: 9
    Last Post: 02-06-2005, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •