    Clivet wsan-xin 71



    Hi
    i have a problem with a clivet wsan-xin 71. the alarm is E020 and it does not reset. Have anybody any idea? thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet wsan-xin 71

    e20 freeze protection- there is a manual reset- check your pumps are working, no air in system and flow switch operates and stops when the pumps stop,sensors display an accurate reading,and setpoint isn't too low

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet wsan-xin 71

    http://www.mediafire.com/view/?c7n1xu5fdd8m5kx similar wsat xee install/service manual

  4. #4
    Join Date
    Jan 2013
    Location
    GREECE
    Age
    44
    Posts
    4
    Rep Power
    0

    Re: Clivet wsan-xin 71

    thanks my friend for your help