    Oil return issue on a commercial system!!



    Hi guys..
    i have been working in industrial ref. industry however recently involved with some commercial projects(HFCs) which i am not so familiar with.Having an oil return issue on a system which has ZR copeland scrolls with R134 a refrigerant!!! any ideas about the root causes!!!

    Appreciated in advance,,,



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Oil return issue on a commercial system!!

    With so much information I wonder why no one hasn't got a clue.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Oil return issue on a commercial system!!

    Hi Bjk.
    the ZR range scrolls are a medium temperature -5.0'C > +5.0'C range compressor,(chillers ) possible problems could be extended high suction pressure conditions, oil separator would then be undersized may require a crankcase pressure regulator. Low suction super heat ( saturated liquid / flood back )