    I am putting together a talk on liquid level controls (LLCs). The basic outline will be an overview of LLCs through the ages, ending with some of the latest technologies and what's on the horizon. Here's my basic outline...

    Early LLC's
    float valves (Phillips, etc)

    Later LLC's
    float switches

    Current LLC's
    capacitance probes, optical sensors

    New & future
    Danfoss wire

    The talk is not intended to promote one company or another. It's for RETA education.

    My question(s)...

    Are there any other LLC's I should be including?

    Do I have the chronological order correct?

    I'm most fuzzy on technologies before float switches and float valves (if there were any). And if I'm missing any of the new or "on the horizon" technologies. Again, not trying to promote any one technology over the other.

    Websites and pictures are a plus. I've been trying to find a picture of an old Magnetrol mercury bulb switch.

    Thanks in advance for your help.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Liquid level controls

    Hi jseidel.
    what's your timeline on this one?
    How soon are you to give the talk?
    Grizzly

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Liquid level controls

    jseidel,
    Another type of measurement is "differential pressure transmitter" which is a lot cheaper to put in.

  4. #4
    Join Date
    Apr 2001
    Location
    The Netherlands
    Age
    63
    Posts
    51
    Rep Power
    24

    Re: Liquid level controls

    I remember a level switch basicly being a thermostat with a heating element from Danfoss(?).
    Don't know the type and all my old documentation has been thrown away few month ago so can't find a copy.
    The principle was that submerged in liquid the bulb would be cooled much more than when not in the liquid.

    Also not in your list are the level transmitters based on Archimedes principle of buoyant force exerted on a body immersed in a liquid like the NI1321 from RTK Kornwestheim.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Liquid level controls

    Check out this link, yes it is a danfoss manual.
    But does refer to many types of level control.
    Albeit modern variants!

    http://www.erawanrefrigeration.co.th...y/Rk0yq102.pdf

    Grizzly

  6. #6
    Join Date
    Apr 2001
    Location
    The Netherlands
    Age
    63
    Posts
    51
    Rep Power
    24

    Re: Liquid level controls

    This is a brochure about the RTK level transmitter that I mentioned:
    http://www.rtk.de/en/produkte0/senso...ansducers.html

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Liquid level controls

    Last edited by chemi-cool; 07-01-2013 at 03:16 PM.

  8. #8
    Join Date
    Mar 2009
    Location
    USA
    Posts
    4
    Rep Power
    0

    Re: Liquid level controls

    Ah...differential pressure transmitter. Good one.

    My talk is next week. So I've got some time.

    Love the old water switch pic. Thanks chemi-cool.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Liquid level controls

    Weka sealed column with floating ball thingo and prox switches, oil column repeating ammonia level,( ammonia only) danfoss teva and sporlan levelmaster are similar principle, danfoss SV pilot float series with PMFL vavs., Hansen pulse width vavs. And way back a little old man regulating hand expansion valve

  10. #10
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Liquid level controls

    Post might be a bit late but we have used Guided Radar level control with good success.

  11. #11
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: Liquid level controls

    I would not even mention the Danfoss wire devices as they clearly do not work and will soon be superceded by some other device from Danfoss.

  12. #12
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: Liquid level controls

    Star refrigeration did a nice one (years back), rather than use a proper float control valve / system on the early LPR systems they used a standard danfoss TEV and cut the Bulb off and soldered this into one of the ports on the system (long time so cant remember where) - this then had system pressure either side of the diaphragm and was used like a float from memory, I think there was an orifice or two involved to slug it......

    We called it a bas******ed TEV for want of a better expression